Thank you, Russell.  Have you had any issues with false starts or any other 
maintenance issues?  The contractor I am working with is trying to investigate 
all possible complications this arrangement might cause.

Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV

Dynamic Fire Designs



Mail: [email protected]
Mobile: 931-242-1299
www.dynamicfiredesigns.com<http://dynamicfiredesigns.com>

Dynamic Fire Designs * 247 Winthrop Dr. * Spring Hill * FL * 34609

This message is confidential. It may also be privileged or otherwise protected 
by work product immunity or other legal rules. If you have received it by 
mistake, please let us know by e-mail reply and delete it from your system; you 
may not copy this message or disclose its contents to anyone. The integrity and 
security of this message cannot be guaranteed on the Internet.


From: Sprinklerforum <[email protected]> On Behalf 
Of Russell Gregory
Sent: Tuesday, April 30, 2019 10:43 PM
To: [email protected]
Subject: RE: Prestart Pump - Preaction

This is the standard arrangement on the Tyco Quell/Vanquish Sprinkler System 
where we start the pump on the 1st stage detection on the Linear Heat 
Detection. A Potter panel is used for control. We also have the pump starting 
on drop in pressure as a backup.
Cheers.
Russell Gregory
Christchurch
New Zealand

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Micah Davis, SET
Sent: Tuesday, 30 April 2019 9:27 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Prestart Pump - Preaction

Has anyone setup a pump on a preaction system to prestart at device signal to 
get it prestarted before valve trip?  I have several large preaction systems 
and am having issues with water delivery times.  I need to shave off a few 
seconds and noticed that the program gives an option to have the pump prestart. 
 We are required on this project to provide the water delivery calculations, so 
I cannot use 7.2.3.4 to avoid the water delivery time requirement.

My specific question is, does anyone know of any concerns the contractor should 
have for doing this?  Are there any operations/maintenance concerns?  Are false 
trips a problem?

Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV

Dynamic Fire Designs



Mail: [email protected]<mailto:[email protected]>
Mobile: 931-242-1299
www.dynamicfiredesigns.com<http://dynamicfiredesigns.com>

Dynamic Fire Designs * 247 Winthrop Dr. * Spring Hill * FL * 34609

This message is confidential. It may also be privileged or otherwise protected 
by work product immunity or other legal rules. If you have received it by 
mistake, please let us know by e-mail reply and delete it from your system; you 
may not copy this message or disclose its contents to anyone. The integrity and 
security of this message cannot be guaranteed on the Internet.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to