Depending on the door opening size and distance of sprinklers to the top of the 
opening, and if the door opening is not protected by a fire door or door that 
would close upon detection of smoke or fire that could prevent combustion gases 
from one side migrating to the other side, then, Yes, you should be calculating 
both systems flowing at the same time.

A fire near the opening could generate heat that would set off the adjacent 
deluge system resulting in both flowing.

I would also be looking at the hazard, if it is a free flowing liquid for 
instance that could flow across the opening, you could also initiate flow from 
both systems.



Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum <[email protected]> On Behalf 
Of Easter, Tim (Contractor)
Sent: Wednesday, May 01, 2019 8:09 AM
To: [email protected]
Subject: [EXTERNAL] deluge system

I have two deluge systems fed from separate risers that have a large door 
opening between the two systems. Am I required to calculate both systems 
flowing.

[cid:[email protected]]

NFPA 13 section 19.2.2 states that areas not separated by a partition shall 
extend 15 feet beyond the more demanding design area. So that means I have to 
flow both deluge systems at the same time, correct?

Best,
Timothy M. Easter


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

Jacobs' Energy, Chemicals and Resources business is now part of Worley

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to