I want to switch this thread to Multi-level ducts.

Why would you provide sprinklers at the intermediate levels?  There is no 
hazard to protect at these levels.  Obviously I am going under the assumption 
there is not a mid-level mezzanine/catwalk/etc.  So with no combustibles and no 
occupancy, there is just open air and nothing specifically to protect.

You already have sprinklers at the roof level protecting everything in the 
space except the floor area obstructed by the ducts over 4ft wide.  Sprinklers 
should be located under the lowest level of ducts to protect the hazard that 
the ceiling sprinklers are obstructed from.  In my opinion, anything beyond 
this is excessive even if the standard doesn’t specifically exclude it, because 
the same can be said in reverse that the standard doesn’t explicitly require it.

Thanks,
Sean VG

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Tuesday, July 2, 2019 7:48 AM
To: [email protected]
Subject: Re: [EXTERNAL] Re: Multi-Level Conveyors

We’ve done the same for multiple layers of ductwork. I just don’t see in the 
standards where I can eliminate because they are multiple levels. I don’t calc 
all levels.


Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=ingy4PBqYPOuUwDLQ4lfaaXSkWsABUV4vTdnAfCdBvU&s=h2a6Ll_6WFL8YiL2bzr5wrZoU1jKivF5Vyu0mMUVaSc&e=>

Sent from my iPhone

On Jul 2, 2019, at 7:31 AM, Kyle.Montgomery 
<[email protected]<mailto:[email protected]>> wrote:
What if it was two levels of ductwork rather than conveyors? Would you protect 
in between the upper and lower ducts, based on that logic?

I’m not saying I disagree with protecting under the upper conveyors in this 
case. I’m just saying that there are always going to be gray areas in the code, 
and that automatically defaulting to the most conservative scenario is 
generally bad for the consumer.

-Kyle M


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Tuesday, July 2, 2019 5:21 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] Re: Multi-Level Conveyors

As I read NFPA 13, it states to place sprinklers under obstructions >48” in 
width. I don’t see anywhere that is states states to place sprinklers only 
under the lowest level of obstructions.

We just finished an addition to a similar facility. It is an FM property. We 
had to do under all of the conveyors (greater than 24” AFF), not just the 
lowest ones.

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign-2Ccom&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=ingy4PBqYPOuUwDLQ4lfaaXSkWsABUV4vTdnAfCdBvU&s=hbawIux7nF3YFtPXdh7S0lfpkJYIZqa82FcCkQChGFQ&e=>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=4oFxlHzjd2d3tMHDTTqbhV7X4Ph3N-I-mON3NVEwxxw&s=xXObiCohsTy-0eYfuDyWmaha2rXEf_XXC0K2ReK2KHs&e=>

Sent from my iPhone

On Jul 2, 2019, at 5:00 AM, John Irwin 
<[email protected]<mailto:[email protected]>> wrote:
We’re protecting a UPS transfer facility and has multi-level conveyors in some 
areas. We have sprinklers under all of the lower level belts but we have a 
questions as to whether we need sprinklers in between the upper levels of 
conveyors. Some UPS facilities have them, some don’t. They don’t have an 
insurance requirement that they are protected. They are all 48” wide.

What say ye?

John Irwin

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=4oFxlHzjd2d3tMHDTTqbhV7X4Ph3N-I-mON3NVEwxxw&s=HPT67TOWfc2Lo54PmXvGsuuG0KcehTJgBzgNCgYAOhw&e=>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=ingy4PBqYPOuUwDLQ4lfaaXSkWsABUV4vTdnAfCdBvU&s=nN6XSjh6hwEHN7MtdhmKjIsaR_WrKMf9GjKdN3vi2kc&e=>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to