And before we go off on a "that's crazy" line of postings regarding my
previous post: I know. It's crazy thinking. But it complies with the rules.


Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)


On Tue, Jul 2, 2019 at 11:04 AM Prahl, Craig/GVL <[email protected]>
wrote:

> I’d have to agree.  Putting sprinklers between layers of general HVAC
> ducts serves no purpose.  Provide sprinklers at the roof above the ducts
> and below the lower most level and be done.  I see no hazard
> justification nor any code language that would require the extra sprinklers
> in between.
>
>
>
>
>
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |
> [email protected] | www.jacobs.com
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Sean.VanGaal
> *Sent:* Tuesday, July 2, 2019 1:52 PM
> *To:* [email protected]
> *Subject:* [EXTERNAL] Multi-Level Ducts
>
>
>
> I want to switch this thread to Multi-level ducts.
>
>
>
> Why would you provide sprinklers at the intermediate levels?  There is no
> hazard to protect at these levels.  Obviously I am going under the
> assumption there is not a mid-level mezzanine/catwalk/etc.  So with no
> combustibles and no occupancy, there is just open air and nothing
> specifically to protect.
>
>
>
> You already have sprinklers at the roof level protecting everything in the
> space except the floor area obstructed by the ducts over 4ft wide.
> Sprinklers should be located under the lowest level of ducts to protect the
> hazard that the ceiling sprinklers are obstructed from.  In my opinion,
> anything beyond this is excessive even if the standard doesn’t specifically
> exclude it, because the same can be said in reverse that the standard
> doesn’t explicitly require it.
>
>
>
> Thanks,
>
> Sean VG
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Travis
> Mack
> *Sent:* Tuesday, July 2, 2019 7:48 AM
> *To:* [email protected]
> *Subject:* Re: [EXTERNAL] Re: Multi-Level Conveyors
>
>
>
> We’ve done the same for multiple layers of ductwork. I just don’t see in
> the standards where I can eliminate because they are multiple levels. I
> don’t calc all levels.
>
>
>
>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> 480-505-9271
>
> MFP Design, LLC
>
> www.mfpdesign,com
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign-2Ccom&d=DwMGaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=0NxwrLm2hhmPFwIzyQzJ6VD-lluYDVF4VIpCSxRVkxA&s=d_lbbhczalPQMQ5RrnXDPkybXj8DsfKnXbtHKLnh49A&e=>
>
> Send large files to MFP Design via:
>
> https://www.hightail.com/u/MFPDesign
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=ingy4PBqYPOuUwDLQ4lfaaXSkWsABUV4vTdnAfCdBvU&s=h2a6Ll_6WFL8YiL2bzr5wrZoU1jKivF5Vyu0mMUVaSc&e=>
>
>
>
> Sent from my iPhone
>
>
> On Jul 2, 2019, at 7:31 AM, Kyle.Montgomery <[email protected]>
> wrote:
>
> What if it was two levels of ductwork rather than conveyors? Would you
> protect in between the upper and lower ducts, based on that logic?
>
>
>
> I’m not saying I disagree with protecting under the upper conveyors in
> this case. I’m just saying that there are always going to be gray areas in
> the code, and that automatically defaulting to the most conservative
> scenario is generally bad for the consumer.
>
>
>
> *-Kyle M*
>
>
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Travis
> Mack
> *Sent:* Tuesday, July 2, 2019 5:21 AM
> *To:* [email protected]
> *Subject:* [EXTERNAL] Re: Multi-Level Conveyors
>
>
>
> As I read NFPA 13, it states to place sprinklers under obstructions >48”
> in width. I don’t see anywhere that is states states to place sprinklers
> only under the lowest level of obstructions.
>
>
>
> We just finished an addition to a similar facility. It is an FM property.
> We had to do under all of the conveyors (greater than 24” AFF), not just
> the lowest ones.
>
>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> 480-505-9271
>
> MFP Design, LLC
>
> www.mfpdesign,com
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign-2Ccom&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=ingy4PBqYPOuUwDLQ4lfaaXSkWsABUV4vTdnAfCdBvU&s=hbawIux7nF3YFtPXdh7S0lfpkJYIZqa82FcCkQChGFQ&e=>
>
> Send large files to MFP Design via:
>
> https://www.hightail.com/u/MFPDesign
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=4oFxlHzjd2d3tMHDTTqbhV7X4Ph3N-I-mON3NVEwxxw&s=xXObiCohsTy-0eYfuDyWmaha2rXEf_XXC0K2ReK2KHs&e=>
>
>
>
> Sent from my iPhone
>
>
> On Jul 2, 2019, at 5:00 AM, John Irwin <[email protected]> wrote:
>
> We’re protecting a UPS transfer facility and has multi-level conveyors in
> some areas. We have sprinklers under all of the lower level belts but we
> have a questions as to whether we need sprinklers in between the upper
> levels of conveyors. Some UPS facilities have them, some don’t. They don’t
> have an insurance requirement that they are protected. They are all 48”
> wide.
>
>
>
> What say ye?
>
>
>
> John Irwin
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=4oFxlHzjd2d3tMHDTTqbhV7X4Ph3N-I-mON3NVEwxxw&s=HPT67TOWfc2Lo54PmXvGsuuG0KcehTJgBzgNCgYAOhw&e=>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=ingy4PBqYPOuUwDLQ4lfaaXSkWsABUV4vTdnAfCdBvU&s=nN6XSjh6hwEHN7MtdhmKjIsaR_WrKMf9GjKdN3vi2kc&e=>
>
>
> ------------------------------
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org