I agree that the ex cov sprinklers can be used. But do you need one listed for Ordinary Hazard or can you use one listed for light hazard.
Spray sprinklers specifically say light is acceptable. Ex cov doesn’t say light is acceptable. Question comes from an owner question. They have OH doors that are 16x14. Current design is 1 spray sprinkler on each side because 14’ max spacing. Owner wants 1 sprinkler. Question is just if can use ex cov sidewall listed for light or do they need to go OH listing. Travis Mack, CFPS, CWBSP, RME-G, SET 480-505-9271 MFP Design, LLC www.mfpdesign,com Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone > On Aug 23, 2019, at 2:21 PM, Mike Stossel via Sprinklerforum > <[email protected]> wrote: > > NFPA 2013 2019 - 11.3.2 (8) Extended coverage sprinklers installed to protect > areas below a single overhead door(s) > > Mike Stossel SET > <image002.png> > 36 Barren Road > East Stroudsburg, PA 18302 > Office: 973-670-2627 > [email protected] > > From: Sprinklerforum <[email protected]> On > Behalf Of Travis Mack via Sprinklerforum > Sent: Friday, August 23, 2019 5:13 PM > To: [email protected] > Cc: Travis Mack <[email protected]> > Subject: Ex cov under OH Door > > Question has been brought up. Can you use ex cov sidewall listed for light > hazard under overhead door in an ordinary hazard building? > > I was under the impression it was not an issue. There is wording in section > on standard spray sidewall that you can. But the same wording is not in the > section under ex cov sidewall sprinklers. Since location has meaning, it made > me question. > > > > Travis Mack, CFPS, CWBSP, RME-G, SET > 480-505-9271 > MFP Design, LLC > www.mfpdesign,com > Send large files to MFP Design via: > https://www.hightail.com/u/MFPDesign > > Sent from my iPhone > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org