Mentoring/Training

I want to demonstrate by way of an example test how each residual pressure/flow 
rate point will fall on the same graphed line on the n1.85 chart.

Thank you,

J. Scott Mitchell, PE
Senior Fire Protection Engineer
Mission Engineering
CNS PTX / Y-12 | 865-576-5258

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Skyler Bilbo via Sprinklerforum
Sent: Wednesday, August 28, 2019 10:03 AM
To: [email protected]
Cc: Skyler Bilbo <[email protected]>
Subject: Re: Water supply test data

A fire pump flow test would typically have this information.  You could just 
look at the inlet pressure and the flow.  The backflow preventer might 
complicate things slightly.  It would be helpful to know why you need this 
information.


Thanks,
Skyler Bilbo

On Wed, Aug 28, 2019 at 8:52 AM Mitchell, Scott via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 wrote:
Does anyone happen to have records of a single water supply test in which 
multiple residual pressures were recorded at multiple flow rates – for example, 
where additional outlets or hydrants are used after the initial flow rate and 
residual pressure are captured?

Any help is appreciated.

Thank you,

J. Scott Mitchell, PE
Senior Fire Protection Engineer
Mission Engineering
CNS PTX / Y-12 | 865-576-5258
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to