This flow test was done in Mattoon, IL:

Pressure    Flow
40 PSI @ 0 GPM
36 PSI @ 376 GPM
27 PSI @ 752 GPM
20 PSI @ 931 GPM


-Skyler



On Wed, Aug 28, 2019 at 9:10 AM Mitchell, Scott via Sprinklerforum <
[email protected]> wrote:

> Mentoring/Training
>
>
>
> I want to demonstrate by way of an example test how each residual
> pressure/flow rate point will fall on the same graphed line on the n1.85
> chart.
>
>
>
> Thank you,
>
>
>
> *J. Scott Mitchell, PE*
>
> *Senior Fire Protection Engineer*
>
> *Mission Engineering*
>
> *CNS PTX / Y-12* | 865-576-5258
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Skyler
> Bilbo via Sprinklerforum
> *Sent:* Wednesday, August 28, 2019 10:03 AM
> *To:* [email protected]
> *Cc:* Skyler Bilbo <[email protected]>
> *Subject:* Re: Water supply test data
>
>
>
> A fire pump flow test would typically have this information.  You could
> just look at the inlet pressure and the flow.  The backflow preventer might
> complicate things slightly.  It would be helpful to know why you need this
> information.
>
>
>
>
>
> Thanks,
>
> Skyler Bilbo
>
>
>
> On Wed, Aug 28, 2019 at 8:52 AM Mitchell, Scott via Sprinklerforum <
> [email protected]> wrote:
>
> Does anyone happen to have records of a single water supply test in which
> multiple residual pressures were recorded at multiple flow rates – for
> example, where additional outlets or hydrants are used after the initial
> flow rate and residual pressure are captured?
>
>
>
> Any help is appreciated.
>
>
>
> Thank you,
>
>
>
> *J. Scott Mitchell, PE*
>
> *Senior Fire Protection Engineer*
>
> *Mission Engineering*
>
> *CNS PTX / Y-12* | 865-576-5258
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to