A talk with the AHJ would be better than  headache later
.
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
[email protected]


On Thu, Oct 24, 2019 at 9:07 PM Kaiser, Richard via Sprinklerforum <
[email protected]> wrote:

> There is no conflict between the documents.
>
>
>
> The 2018 IFC commentary is indeed very explicit, but it does NOT say that
> the allowable omission of sprinklers in certain areas negates the building
> as being considered sprinklered throughout.  In fact, it says the opposite.
>
>
>
> From 2018 IFC with Commentary:
>
> 903.3.1.1 NFPA 13 sprinkler systems.
>
> “Because installation is required to be in accordance with NFPA 13, if the
> standard allows for the omission of sprinklers in any location, then the
> building is still considered as sprinklered throughout.”
>
>
>
> 903.3.1.1.1 Exempt locations.
>
> “This section allows the omission of sprinkler protection in certain
> locations if an approved automatic fire detection system is installed.
> Buildings in compliance with one of the six listed conditions would still
> be considered fully sprinklered throughout in compliance with the code and
> NFPA 13 and thus are eligible for all applicable code alternatives,
> exceptions or reductions.”
>
>
>
> *Richard* *Kaiser* PE
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Prahl, Craig/GVL via Sprinklerforum
> *Sent:* Thursday, October 24, 2019 1:20 PM
> *To:* [email protected]; James Litvak <
> [email protected]>
> *Cc:* Prahl, Craig/GVL <[email protected]>; Hinson, Ryan <
> [email protected]>
> *Subject:* RE: [EXTERNAL] Trying to determine hydrant locations per IFC,
> wondering how sprinkler coverage omissions will affect distances.
>
>
>
> In the 2018 IFC commentary the language is very explicit in that omission
> of sprinklers no longer qualifies a building as being fully sprinklered and
> you lose the ability to apply any allowances the code gives if the building
> was fully sprinklered.
>
>
>
> Installed throughout means installed throughout.
>
>
>
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |
> [email protected] | www.jacobs.com
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Hinson, Ryan via Sprinklerforum
> *Sent:* Thursday, October 24, 2019 1:57 PM
> *To:* James Litvak <[email protected]>;
> [email protected]
> *Cc:* Hinson, Ryan <[email protected]>
> *Subject:* RE: [EXTERNAL] Trying to determine hydrant locations per IFC,
> wondering how sprinkler coverage omissions will affect distances.
>
>
>
> James,
>
>
>
> From IBC 2018 commentary:
>
> *Section 202*
>
> *DEFINITIONS*
>
> *[F] AUTOMATIC SPRINKLER SYSTEM*. *An automatic sprinkler system*, for
> fire protection purposes, is an integrated system of underground and
> overhead piping designed in accordance with fire protection engineering
> standards. The system includes a suitable water supply. The portion of the
> system above the ground is a network of specially sized or hydraulically
> designed piping installed in a structure or area, generally overhead, and
> to which *automatic* sprinklers are connected in a systematic pattern.
> The system is usually activated by heat from a fire and discharges water
> over the fire area.
>
>    - An automatic sprinkler system is one type of automatic
>    fire-extinguishing system. Automatic sprinkler systems are the most common,
>    and their life safety attributes are widely recognized. The code specifies
>    three types of automatic sprinkler systems: one installed in accordance
>    with NFPA 13, one in accordance with NFPA 13R and the other in accordance
>    with NFPA 13D. To be considered for most code design alternatives, a
>    building’s automatic sprinkler system must be installed throughout in
>    accordance with NFPA 13 (see Section 903.3.1.1).
>
> In a fire, sprinklers automatically open and discharge water onto the fire
> in a spray pattern that is designed to contain or extinguish the fire.
> Originally, automatic sprinkler systems were developed just for the
> protection of buildings and their contents. Because of the development and
> improvements in sprinkler head response time and water distribution,
> however, automatic sprinkler systems are now also considered life safety
> systems. Proper operation of an automatic sprinkler system requires careful
> selection of the sprinkler heads so that water in sufficient quantity, at
> adequate pressure and  properly distributed will be available to suppress
> the fire. Note that he use of the term “fire area” in the last sentence of
> the definition refers to the area in which the fire is occurring, not to
> the defined term “Fire area.”
>
> There are many different types of automatic sprinkler systems—wet pipe,
> dry pipe, preaction, anti-freeze and various combinations. Sprinklers can
> be pendant, upright or sidewall and can be designed for standard or
> extended coverage. Additional information can be found in NFPA 13.
>
>
>
> *Section 903*
>
> *AUTOMATIC SPRINKLER SYSTEMS*
>
>
>
> *[F] 903.3 Installation requirements*. *Automatic sprinkler systems*
> shall be designed and installed in accordance with Sections 903.3.1 through
> 903.3.8.
>
> *[F] 903.3.1 Standards*. Sprinkler systems shall be designed and
> installed in accordance with Section 903.3.1.1 unless otherwise permitted
> by Sections 903.3.1.2 and 903.3.1.3 and other chapters of this code, as
> applicable.
>
> * [F] 903.3.1.1 NFPA 13 sprinkler systems*. Where the provisions of this
> code require that a building or portion thereof be equipped throughout with
> an *automatic sprinkler system* in accordance with this section,
> sprinklers shall be installed throughout in accordance with NFPA 13 except
> as provided in Sections 903.3.1.1.1 and 903.3.1.1.2.
>
>    - NFPA 13 contains the minimum requirements for the design and
>    installation of automatic water sprinkler systems and exposure protection
>    sprinkler systems. The requirements contained in the standard include the
>    character and adequacy of the water supply and the selection of sprinklers,
>    piping, valves and all of the materials and accessories. The standard does
>    not include requirements for installation of private fire service mains and
>    their appurtenances, installation of fire pumps, or construction and
>    installation of gravity and pressure tanks and towers.
>
> NFPA 13 defines seven classifications or types of water sprinkler systems:
> wet pipe [see Commentary Figure 903.3.1.1], dry pipe, preaction or deluge,
> combined dry pipe and preaction, antifreeze systems, sprinkler systems that
> are designed for a special purpose and outside sprinklers for exposure
> protection. While numerous variables must be considered in selecting the
> proper type of sprinkler system, the wet-pipe sprinkler system is
> recognized as the most effective and efficient. The wet-pipe system is also
> the most reliable type of sprinkler system because water under pressure is
> available at the sprinkler. Therefore, wet-pipe sprinkler systems are
> recommended wherever possible.
>
> The extent of coverage and distribution of sprinklers is based on the NFPA
> 13 standard. Numerous conditions exist in the standard where sprinklers are
> specifically required and also where they may or may not be located. Once
> it is determined that the sprinkler system is to be in accordance with NFPA
> 13, that standard must be reviewed for installation details. For example,
> exterior spaces such as combustible canopies are required to be equipped
> with sprinklers according to Section 8.15.7 of NFPA 13 where the canopy
> extends for a distance of 4 feet (1219 mm) or more. A 3-foot (914 mm)
> combustible canopy would not require sprinklers nor would a 6-foot (1829
> mm) canopy constructed of noncombustible materials, provided there is no
> combustible storage under the canopy.
>
> Because installation is required to be in accordance with NFPA 13, if the
> standard allows for the omission of sprinklers in any location, then the
> building is still considered as sprinklered throughout. For example,
> Section 8.15.8.1.1 of NFPA 13 allows sprinklers to be omitted from
> bathrooms in dwelling units in motels and hotels. If sprinklers are not
> provided in the bathrooms because of the conditions stipulated in NFPA 13,
> the building would still be considered as sprinklered throughout in
> accordance with the code, NFPA 13 and the IFC.
>
> Exceptions for the use of NFPA 13R and 13D systems are addressed
> throughout the code when exceptions based on the use of sprinklers are
> provided. More specifically, if the use of these other standards is
> appropriate, it will be noted within the exception. For a building to be
> considered “equipped throughout” with an NFPA 13 sprinkler system, complete
> protection must be provided in accordance with the referenced standard,
> subject to the exempt locations indicated in Section 903.3.1.1.1. See
> Commentary Figure 904.2.1 for examples of requirements modified through the
> use of sprinkler systems.
>
> *[F] 903.3.1.1.1 Exempt locations*. Automatic sprinklers shall not be
> required in the following rooms or areas where such rooms or areas are
> protected with an *approved* automatic fire detection system in
> accordance with Section 907.2 that will respond to visible or invisible
> particles of combustion. Sprinklers shall not be omitted from a room merely
> because it is damp, of fire-resistance-rated construction or contains
> electrical equipment.
>
> 1. A room where the application of water, or flame and water, constitutes
> a serious life or fire hazard.
>
> 2. A room or space where sprinklers are considered undesirable because of
> the nature of the contents, where *approved* by the fire code official.
>
> 3. Generator and transformer rooms separated from the remainder of the
> building by walls and floor/ceiling or roof/ceiling assemblies having a 
> *fire-resistance
> rating* of not less than 2 hours.
>
> 4. Rooms or areas that are of noncombustible construction with wholly
> noncombustible contents.
>
> 5. Fire service access elevator machine rooms and machinery spaces.
>
> 6. Machine rooms, machinery spaces, control rooms and control spaces
> associated with occupant evacuation elevators designed in accordance with
> Section 3008.
>
>    - This section allows the omission of sprinkler protection in certain
>       locations if an approved automatic fire detection system is installed. 
> Buildings
>       in compliance with one of the six listed conditions would still be
>       considered fully sprinklered throughout in compliance with the code and
>       NFPA 13 and thus are eligible for all applicable code alternatives,
>       exceptions or reductions. Elimination of the sprinkler system in a
>       sensitive area is subject to the approval of the fire code official.
>
> Condition 1 addresses restrictions where the application of water could
> create a hazardous condition. For example, sprinkler protection is to be
> avoided where it is not compatible with certain stored materials (i.e.,
> some water-reactive hazardous materials such as calcium carbide).
> Combustible metals, such as magnesium and aluminum, may burn so intensely
> that the use of water to attempt fire control will only intensify the
> reaction.
>
> It is not the intent of Condition 2 to omit sprinklers solely because of a
> potential for water damage. A desire to not sprinkler a certain area (such
> as a computer room or operating room) does not fall within the limitations
> of the exception unless there is something unique about the space that
> would result in water being incompatible. A computer room can be adequately
> protected using an automatic sprinkler system or an alternative gaseous
> suppression agent system or a combination of these systems. The intent of
> Condition 2 is to consider whether the contents would react adversely to
> the application of water. It is important to note that the fire code
> official must approve the use of this item. Note also that with respect to
> computer rooms, NFPA 75 (Protection of Information Technology Equipment)
> (not a referenced standard) recognizes automatic sprinklers as the primary
> fire protection system for computer rooms.
>
> Condition 3 recognizes the low fuel load and low occupancy hazards
> associated with generator and transformer rooms and, therefore, allows the
> omission of sprinkler protection if the rooms are separated from adjacent
> areas by 2-hour fire-resistance-rated construction. This condition assumes
> the room is not used for any combustible storage. This condition is similar
> to Section 8.15.11.3 of NFPA 13, which exempts electrical equipment rooms
> from sprinkler protection, provided the room is dedicated to the use of
> dry-type electrical equipment, is constructed as a 2-hour
> fire-resistance-rated enclosure, and is not used for combustible storage.
>
> Condition 4 requires the construction of the room or area, as well as the
> contents, to be noncombustible. An example would be an area in an
> unprotected steel-frame building (Type IIB construction) used for steel or
> concrete block storage. Neither involves any significant combustible
> packaging or sources of ignition, and few combustibles are present (see
> Commentary Figure 903.3.1).
>
> Condition 5 addresses the concern for elevator machine rooms and machinery
> spaces associated with fire service access elevators as required by
> Sections 403.6.1 and 3007, for buildings with occupied floors greater than
> 120 feet (36.58 m) from the lowest level of fire department access. These
> elevators need to work during fire situations and their operation cannot be
> threatened by the activation of a sprinkler in a machine room or space that
> may affect the operation of the elevators. Fire service access elevators
> are required to be continuously monitored at the fire command center in
> accordance with Section 3007.7.
>
> Condition 6, similar to Condition 5, exempts sprinklers from the machine
> rooms, machinery spaces, control rooms and control spaces for occupant
> evacuation elevators. Like fire service access elevators, these elevators
> need to work during fire situations and their operation cannot be
>  threatened by the activation of a sprinkler in machine rooms, machinery
> spaces, control rooms and control spaces. Such elevators are required to be
> monitored at the fire command center in accordance with Section 3008.7.
>
>
>
> Hope this helps,
>
>
>
> *Ryan L. Hinson**, PE*, SET***  \  Burns & McDonnell
>
> Senior Fire Protection Engineer
>
> *O* 952-656-3662 \  *M* 320-250-5404  \  *F* 952-229-2923
>
> *[email protected] <[email protected]>*  \  burnsmcd.com
> <https://urldefense.com/v3/__http:/www.burnsmcd.com/__;!dEgXJxch11IPYA!RT2Dan24-blBx6PbP9F5YSqsHwudRJtCo63dneAwp5Cc666fkjRZNtqDijCxSbl2lA$>
>
> 8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
>
> *Registered in: LA, MD, MN, PA, TX, & UT
>
> **NICET IV - Water-Based Systems Layout
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *James Litvak via Sprinklerforum
> *Sent:* Thursday, October 24, 2019 12:14 PM
> *To:* Prahl, Craig/GVL <[email protected]>
> *Cc:* James Litvak <[email protected]>;
> [email protected]
> *Subject:* Re: [EXTERNAL] Trying to determine hydrant locations per IFC,
> wondering how sprinkler coverage omissions will affect distances.
>
>
>
> Interesting. I don't have access to a copy of the Code and Commentary.
> Would you be able to copy/paste the relevant section, or tell me where to
> find it? I will try to get access to it.
>
> Thanks.
>
>
>
> On Thu, Oct 24, 2019 at 12:35 PM Prahl, Craig/GVL <[email protected]>
> wrote:
>
> Nope, the omission of sprinklers by any means or allowances null and voids
> the “sprinklered throughout” classification.  That is addressed within the
> IBC Commentary.  Just had this discussion on a project myself.
>
>
>
> It is the same if you substitute a clean agent for sprinklers in an area.
> No longer considered sprinklered throughout.
>
>
>
>
>
>
>
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |
> [email protected] | www.jacobs.com
> <https://urldefense.com/v3/__https:/nam05.safelinks.protection.outlook.com/?url=http*3A*2F*2Fwww.jacobs.com*2F&data=02*7C01*7Crhinson*40burnsmcd.com*7Ce32d5bc887a341f2e32708d758a5924a*7Cbfbb9a2b6d994e78b3c795005d555c8b*7C0*7C0*7C637075340466060912&sdata=hvSGYJcGlCnfvsXoOBaFMYhCH4mN5A9nvyQMHKaHSgM*3D&reserved=0__;JSUlJSUlJSUlJSUlJQ!dEgXJxch11IPYA!RT2Dan24-blBx6PbP9F5YSqsHwudRJtCo63dneAwp5Cc666fkjRZNtqDijBwRS198A$>
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *James Litvak via Sprinklerforum
> *Sent:* Thursday, October 24, 2019 12:18 PM
> *To:* [email protected]
> *Cc:* James Litvak <[email protected]>
> *Subject:* [EXTERNAL] Trying to determine hydrant locations per IFC,
> wondering how sprinkler coverage omissions will affect distances.
>
>
>
> I'm working on a manufacturing facility that is building type IIB. Per the
> fire-flow requirement of 8,000 gpm, the average spacing of hydrants will
> need to be 200 feet, per IFC Table C102.1. However, note f will allow a
> 50-percent spacing increase if "the building is equipped *throughout* with
> an automatic sprinkler system in accordance with Section 903.3.1.1 of the 
> *International
> Fire Code*" (emphasis mine). The reason I bolded throughout is because
> approximately 2/3 of the building has sprinklers omitted in accordance with
> exceptions from Section 903.3.1.1. So my question is, if Section 903.3.1.1
> is being followed such that it is being applied throughout the building,
> and the areas of the building that aren't being sprinklered are allowed by
> that section, does this count as "equipped throughout"?
>
>
> ------------------------------
>
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
>
>
> ------------------------------
>
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to