I’d agree with Ed. It is likely quite a bit of conversation has already 
occurred. The reviewer is already trying to get to minimum needed.

Best.

Bruce Verhei 

> On Oct 24, 2019, at 21:44, Ed Vining via Sprinklerforum 
> <[email protected]> wrote:
> 
> A talk with the AHJ would be better than  headache later
> .
> Ed Vining
> 4819 John Muir Rd
> Martinez CA 94553
> 925-228-8792
> [email protected]
> 
> 
>> On Thu, Oct 24, 2019 at 9:07 PM Kaiser, Richard via Sprinklerforum 
>> <[email protected]> wrote:
>> There is no conflict between the documents.
>> 
>>  
>> 
>> The 2018 IFC commentary is indeed very explicit, but it does NOT say that 
>> the allowable omission of sprinklers in certain areas negates the building 
>> as being considered sprinklered throughout.  In fact, it says the opposite.
>> 
>>  
>> 
>> From 2018 IFC with Commentary:
>> 
>> 903.3.1.1 NFPA 13 sprinkler systems.
>> 
>> “Because installation is required to be in accordance with NFPA 13, if the 
>> standard allows for the omission of sprinklers in any location, then the 
>> building is still considered as sprinklered throughout.”
>> 
>>  
>> 
>> 903.3.1.1.1 Exempt locations.
>> 
>> “This section allows the omission of sprinkler protection in certain 
>> locations if an approved automatic fire detection system is installed. 
>> Buildings in compliance with one of the six listed conditions would still be 
>> considered fully sprinklered throughout in compliance with the code and NFPA 
>> 13 and thus are eligible for all applicable code alternatives, exceptions or 
>> reductions.”
>> 
>>  
>> 
>> Richard Kaiser PE
>> 
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Prahl, Craig/GVL via Sprinklerforum
>> Sent: Thursday, October 24, 2019 1:20 PM
>> To: [email protected]; James Litvak 
>> <[email protected]>
>> Cc: Prahl, Craig/GVL <[email protected]>; Hinson, Ryan 
>> <[email protected]>
>> Subject: RE: [EXTERNAL] Trying to determine hydrant locations per IFC, 
>> wondering how sprinkler coverage omissions will affect distances.
>> 
>>  
>> 
>> In the 2018 IFC commentary the language is very explicit in that omission of 
>> sprinklers no longer qualifies a building as being fully sprinklered and you 
>> lose the ability to apply any allowances the code gives if the building was 
>> fully sprinklered. 
>> 
>>  
>> 
>> Installed throughout means installed throughout.
>> 
>>  
>> 
>> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
>> [email protected] | www.jacobs.com
>> 
>> 1041 East Butler Road   Greenville, South Carolina  29606
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Hinson, Ryan via Sprinklerforum
>> Sent: Thursday, October 24, 2019 1:57 PM
>> To: James Litvak <[email protected]>; 
>> [email protected]
>> Cc: Hinson, Ryan <[email protected]>
>> Subject: RE: [EXTERNAL] Trying to determine hydrant locations per IFC, 
>> wondering how sprinkler coverage omissions will affect distances.
>> 
>>  
>> 
>> James,
>> 
>>  
>> 
>> From IBC 2018 commentary:
>> 
>> Section 202
>> 
>> DEFINITIONS
>> 
>> [F] AUTOMATIC SPRINKLER SYSTEM. An automatic sprinkler system, for fire 
>> protection purposes, is an integrated system of underground and overhead 
>> piping designed in accordance with fire protection engineering standards. 
>> The system includes a suitable water supply. The portion of the system above 
>> the ground is a network of specially sized or hydraulically designed piping 
>> installed in a structure or area, generally overhead, and to which automatic 
>> sprinklers are connected in a systematic pattern. The system is usually 
>> activated by heat from a fire and discharges water over the fire area.
>> 
>> An automatic sprinkler system is one type of automatic fire-extinguishing 
>> system. Automatic sprinkler systems are the most common, and their life 
>> safety attributes are widely recognized. The code specifies three types of 
>> automatic sprinkler systems: one installed in accordance with NFPA 13, one 
>> in accordance with NFPA 13R and the other in accordance with NFPA 13D. To be 
>> considered for most code design alternatives, a building’s automatic 
>> sprinkler system must be installed throughout in accordance with NFPA 13 
>> (see Section 903.3.1.1).
>> In a fire, sprinklers automatically open and discharge water onto the fire 
>> in a spray pattern that is designed to contain or extinguish the fire. 
>> Originally, automatic sprinkler systems were developed just for the 
>> protection of buildings and their contents. Because of the development and 
>> improvements in sprinkler head response time and water distribution, 
>> however, automatic sprinkler systems are now also considered life safety 
>> systems. Proper operation of an automatic sprinkler system requires careful 
>> selection of the sprinkler heads so that water in sufficient quantity, at 
>> adequate pressure and  properly distributed will be available to suppress 
>> the fire. Note that he use of the term “fire area” in the last sentence of 
>> the definition refers to the area in which the fire is occurring, not to the 
>> defined term “Fire area.”
>> 
>> There are many different types of automatic sprinkler systems—wet pipe, dry 
>> pipe, preaction, anti-freeze and various combinations. Sprinklers can be 
>> pendant, upright or sidewall and can be designed for standard or extended 
>> coverage. Additional information can be found in NFPA 13.
>> 
>>  
>> 
>> Section 903
>> 
>> AUTOMATIC SPRINKLER SYSTEMS
>> 
>>  
>> 
>> [F] 903.3 Installation requirements. Automatic sprinkler systems shall be 
>> designed and installed in accordance with Sections 903.3.1 through 903.3.8.
>> 
>> [F] 903.3.1 Standards. Sprinkler systems shall be designed and installed in 
>> accordance with Section 903.3.1.1 unless otherwise permitted by Sections 
>> 903.3.1.2 and 903.3.1.3 and other chapters of this code, as applicable.
>> 
>>  [F] 903.3.1.1 NFPA 13 sprinkler systems. Where the provisions of this code 
>> require that a building or portion thereof be equipped throughout with an 
>> automatic sprinkler system in accordance with this section, sprinklers shall 
>> be installed throughout in accordance with NFPA 13 except as provided in 
>> Sections 903.3.1.1.1 and 903.3.1.1.2.
>> 
>> NFPA 13 contains the minimum requirements for the design and installation of 
>> automatic water sprinkler systems and exposure protection sprinkler systems. 
>> The  requirements contained in the standard include the character and 
>> adequacy of the water supply and the selection of sprinklers, piping, valves 
>> and all of the materials and accessories. The standard does not include 
>> requirements for installation of private fire service mains and their 
>> appurtenances, installation of fire pumps, or construction and installation 
>> of gravity and pressure tanks and towers.
>> NFPA 13 defines seven classifications or types of water sprinkler systems: 
>> wet pipe [see Commentary Figure 903.3.1.1], dry pipe, preaction or deluge, 
>> combined dry pipe and preaction, antifreeze systems, sprinkler systems that 
>> are designed for a special purpose and outside sprinklers for exposure 
>> protection. While numerous variables must be considered in selecting the 
>> proper type of sprinkler system, the wet-pipe sprinkler system is recognized 
>> as the most effective and efficient. The wet-pipe system is also the most 
>> reliable type of sprinkler system because water under pressure is available 
>> at the sprinkler. Therefore, wet-pipe sprinkler systems are recommended 
>> wherever possible.
>> 
>> The extent of coverage and distribution of sprinklers is based on the NFPA 
>> 13 standard. Numerous conditions exist in the standard where sprinklers are 
>> specifically required and also where they may or may not be located. Once it 
>> is determined that the sprinkler system is to be in accordance with NFPA 13, 
>> that standard must be reviewed for installation details. For example, 
>> exterior spaces such as combustible canopies are required to be equipped 
>> with sprinklers according to Section 8.15.7 of NFPA 13 where the canopy 
>> extends for a distance of 4 feet (1219 mm) or more. A 3-foot (914 mm) 
>> combustible canopy would not require sprinklers nor would a 6-foot (1829 mm) 
>> canopy constructed of noncombustible materials, provided there is no 
>> combustible storage under the canopy.
>> 
>> Because installation is required to be in accordance with NFPA 13, if the 
>> standard allows for the omission of sprinklers in any location, then the 
>> building is still considered as sprinklered throughout. For example, Section 
>> 8.15.8.1.1 of NFPA 13 allows sprinklers to be omitted from bathrooms in 
>> dwelling units in motels and hotels. If sprinklers are not provided in the 
>> bathrooms because of the conditions stipulated in NFPA 13, the building 
>> would still be considered as sprinklered throughout in accordance with the 
>> code, NFPA 13 and the IFC.
>> 
>> Exceptions for the use of NFPA 13R and 13D systems are addressed throughout 
>> the code when exceptions based on the use of sprinklers are provided. More 
>> specifically, if the use of these other standards is appropriate, it will be 
>> noted within the exception. For a building to be considered “equipped 
>> throughout” with an NFPA 13 sprinkler system, complete protection must be 
>> provided in accordance with the referenced standard, subject to the exempt 
>> locations indicated in Section 903.3.1.1.1. See Commentary Figure 904.2.1 
>> for examples of requirements modified through the use of sprinkler systems.
>> 
>> [F] 903.3.1.1.1 Exempt locations. Automatic sprinklers shall not be required 
>> in the following rooms or areas where such rooms or areas are protected with 
>> an approved automatic fire detection system in accordance with Section 907.2 
>> that will respond to visible or invisible particles of combustion. 
>> Sprinklers shall not be omitted from a room merely because it is damp, of 
>> fire-resistance-rated construction or contains electrical equipment.
>> 
>> 1. A room where the application of water, or flame and water, constitutes a 
>> serious life or fire hazard.
>> 
>> 2. A room or space where sprinklers are considered undesirable because of 
>> the nature of the contents, where approved by the fire code official.
>> 
>> 3. Generator and transformer rooms separated from the remainder of the 
>> building by walls and floor/ceiling or roof/ceiling assemblies having a 
>> fire-resistance rating of not less than 2 hours.
>> 
>> 4. Rooms or areas that are of noncombustible construction with wholly 
>> noncombustible contents.
>> 
>> 5. Fire service access elevator machine rooms and machinery spaces.
>> 
>> 6. Machine rooms, machinery spaces, control rooms and control spaces 
>> associated with occupant evacuation elevators designed in accordance with 
>> Section 3008.
>> 
>> This section allows the omission of sprinkler protection in certain 
>> locations if an approved automatic fire detection system is installed. 
>> Buildings in compliance with one of the six listed conditions would still be 
>> considered fully sprinklered throughout in compliance with the code and NFPA 
>> 13 and thus are eligible for all applicable code alternatives, exceptions or 
>> reductions. Elimination of the sprinkler system in a sensitive area is 
>> subject to the approval of the fire code official.
>> Condition 1 addresses restrictions where the application of water could 
>> create a hazardous condition. For example, sprinkler protection is to be 
>> avoided where it is not compatible with certain stored materials (i.e., some 
>> water-reactive hazardous materials such as calcium carbide). Combustible 
>> metals, such as magnesium and aluminum, may burn so intensely that the use 
>> of water to attempt fire control will only intensify the reaction.
>> 
>> It is not the intent of Condition 2 to omit sprinklers solely because of a 
>> potential for water damage. A desire to not sprinkler a certain area (such 
>> as a computer room or operating room) does not fall within the limitations 
>> of the exception unless there is something unique about the space that would 
>> result in water being incompatible. A computer room can be adequately 
>> protected using an automatic sprinkler system or an alternative gaseous 
>> suppression agent system or a combination of these systems. The intent of 
>> Condition 2 is to consider whether the contents would react adversely to the 
>> application of water. It is important to note that the fire code official 
>> must approve the use of this item. Note also that with respect to computer 
>> rooms, NFPA 75 (Protection of Information Technology Equipment) (not a 
>> referenced standard) recognizes automatic sprinklers as the primary fire 
>> protection system for computer rooms.
>> 
>> Condition 3 recognizes the low fuel load and low occupancy hazards 
>> associated with generator and transformer rooms and, therefore, allows the 
>> omission of sprinkler protection if the rooms are separated from adjacent 
>> areas by 2-hour fire-resistance-rated construction. This condition assumes 
>> the room is not used for any combustible storage. This condition is similar 
>> to Section 8.15.11.3 of NFPA 13, which exempts electrical equipment rooms 
>> from sprinkler protection, provided the room is dedicated to the use of 
>> dry-type electrical equipment, is constructed as a 2-hour 
>> fire-resistance-rated enclosure, and is not used for combustible storage.
>> 
>> Condition 4 requires the construction of the room or area, as well as the 
>> contents, to be noncombustible. An example would be an area in an 
>> unprotected steel-frame building (Type IIB construction) used for steel or 
>> concrete block storage. Neither involves any significant combustible 
>> packaging or sources of ignition, and few combustibles are present (see 
>> Commentary Figure 903.3.1).
>> 
>> Condition 5 addresses the concern for elevator machine rooms and machinery 
>> spaces associated with fire service access elevators as required by Sections 
>> 403.6.1 and 3007, for buildings with occupied floors greater than 120 feet 
>> (36.58 m) from the lowest level of fire department access. These elevators 
>> need to work during fire situations and their operation cannot be threatened 
>> by the activation of a sprinkler in a machine room or space that may affect 
>> the operation of the elevators. Fire service access elevators are required 
>> to be continuously monitored at the fire command center in accordance with 
>> Section 3007.7.
>> 
>> Condition 6, similar to Condition 5, exempts sprinklers from the machine 
>> rooms, machinery spaces, control rooms and control spaces for occupant 
>> evacuation elevators. Like fire service access elevators, these elevators 
>> need to work during fire situations and their operation cannot be  
>> threatened by the activation of a sprinkler in machine rooms, machinery 
>> spaces, control rooms and control spaces. Such elevators are required to be 
>> monitored at the fire command center in accordance with Section 3008.7.
>> 
>>  
>> 
>> Hope this helps,
>> 
>>  
>> 
>> Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
>> 
>> Senior Fire Protection Engineer
>> 
>> O 952-656-3662 \  M 320-250-5404  \  F 952-229-2923
>> 
>> [email protected]  \  burnsmcd.com
>> 
>> 8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
>> 
>> *Registered in: LA, MD, MN, PA, TX, & UT
>> 
>> **NICET IV - Water-Based Systems Layout
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of James Litvak via Sprinklerforum
>> Sent: Thursday, October 24, 2019 12:14 PM
>> To: Prahl, Craig/GVL <[email protected]>
>> Cc: James Litvak <[email protected]>; 
>> [email protected]
>> Subject: Re: [EXTERNAL] Trying to determine hydrant locations per IFC, 
>> wondering how sprinkler coverage omissions will affect distances.
>> 
>>  
>> 
>> Interesting. I don't have access to a copy of the Code and Commentary. Would 
>> you be able to copy/paste the relevant section, or tell me where to find it? 
>> I will try to get access to it. 
>> 
>> Thanks. 
>> 
>>  
>> 
>> On Thu, Oct 24, 2019 at 12:35 PM Prahl, Craig/GVL <[email protected]> 
>> wrote:
>> 
>> Nope, the omission of sprinklers by any means or allowances null and voids 
>> the “sprinklered throughout” classification.  That is addressed within the 
>> IBC Commentary.  Just had this discussion on a project myself.
>> 
>>  
>> 
>> It is the same if you substitute a clean agent for sprinklers in an area.  
>> No longer considered sprinklered throughout.
>> 
>>  
>> 
>>  
>> 
>>  
>> 
>> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
>> [email protected] | www.jacobs.com
>> 
>> 1041 East Butler Road   Greenville, South Carolina  29606
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of James Litvak via Sprinklerforum
>> Sent: Thursday, October 24, 2019 12:18 PM
>> To: [email protected]
>> Cc: James Litvak <[email protected]>
>> Subject: [EXTERNAL] Trying to determine hydrant locations per IFC, wondering 
>> how sprinkler coverage omissions will affect distances.
>> 
>>  
>> 
>> I'm working on a manufacturing facility that is building type IIB. Per the 
>> fire-flow requirement of 8,000 gpm, the average spacing of hydrants will 
>> need to be 200 feet, per IFC Table C102.1. However, note f will allow a 
>> 50-percent spacing increase if "the building is equipped throughout with an 
>> automatic sprinkler system in accordance with Section 903.3.1.1 of the 
>> International Fire Code" (emphasis mine). The reason I bolded throughout is 
>> because approximately 2/3 of the building has sprinklers omitted in 
>> accordance with exceptions from Section 903.3.1.1. So my question is, if 
>> Section 903.3.1.1 is being followed such that it is being applied throughout 
>> the building, and the areas of the building that aren't being sprinklered 
>> are allowed by that section, does this count as "equipped throughout"?  
>> 
>>  
>> 
>> 
>> NOTICE - This communication may contain confidential and privileged 
>> information that is for the sole use of the intended recipient. Any viewing, 
>> copying or distribution of, or reliance on this message by unintended 
>> recipients is strictly prohibited. If you have received this message in 
>> error, please notify us immediately by replying to the message and deleting 
>> it from your computer.
>> 
>>  
>> 
>> 
>> NOTICE - This communication may contain confidential and privileged 
>> information that is for the sole use of the intended recipient. Any viewing, 
>> copying or distribution of, or reliance on this message by unintended 
>> recipients is strictly prohibited. If you have received this message in 
>> error, please notify us immediately by replying to the message and deleting 
>> it from your computer.
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to