The standard doesn’t really address this condition, but I think it’s consistent 
with the intent and firefighting strategies that if you have to add a 250 GPM 
allowance for a standpipe that’s only serving one side of a 2-hour building 
separation, you would add it to the demand on the valve side of the separation 
because that is where they’d be coming from.    But ultimately, it might be 
best to add it to whichever fire area would create the highest demand.    The 
standard informs that when a single structure is divided into two or more 
“buildings” by such separations, you have to meet all the demands if they are 
taken as separate buildings.   So if one area is large enough to require three 
standpipes, then you’d need to prove 1,000 GPM for that area and lower flows 
for the others.

MY OPINION ONLY.

Steve Leyton

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Zachary Siegrist via Sprinklerforum
Sent: Tuesday, January 21, 2020 1:15 PM
To: [email protected]
Cc: Zachary Siegrist
Subject: standpipe horizontal exit calculation question

In a building recognized as part of separate fire areas, the annex material in 
NFPA 14 Section 7.10.1.1 states the the total supply can be calculated based on 
the single bldg/ fire area requiring the greatest number of standpipes.  In 
this scenario, the physical separation between fire areas is functioning as a 
horizontal exit requiring a hose valves at the horizontal exit.  One side of 
the wall meets the 100 ft. + 30 ft. hose stream exemption while the other side 
does not.  The hose valves will be fed via an independent vertical standpipe 
riser.
Is this hose valve located at the horizontal exit calculated as part of the 
area it is located in or calculated as part of the building it serves on the 
opposite side of the horizontal exit?   I thought this was addressed somewhere 
in 14 but I can't locate it.

Can anyone help me out this afternoon?

Zach




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to