Such construction is difficult to reconcile on the FP side when the design 
team, including the structural team, is told the structure between building A 
and building B is essentially a third structure and the two buildings are to be 
built such that one side can burn and fall away without affecting the other 
building.

> On Jan 24, 2020, at 10:51 AM, Pete Schwab via Sprinklerforum 
> <[email protected]> wrote:
> 
> This may be what you are looking for if you have horizontal exits.
>  
>  
>  
> <image001.png>
>  
>  
> <image002.png>
>  
> Peter Schwab
> VP of Purchasing and Engineering technologies
>  
> Wayne Automatic Fire Sprinklers Inc.
> 222 Capitol Court
> Ocoee, Fl 34761
>  
> Mobile: (407) 468-8248
> Direct: (407) 877-5570
> Fax: (407) 656-8026
>  
> www.waynefire.com <http://www.waynefire.com/>
>  
> <image003.jpg>
>  
> <image004.png>
>  
> I sleep in a sprinklered home, do you? 
>  
>  
> From: Sprinklerforum <[email protected] 
> <mailto:[email protected]>> On Behalf Of Steve 
> Leyton via Sprinklerforum
> Sent: Wednesday, January 22, 2020 12:38 PM
> To: [email protected] 
> <mailto:[email protected]>
> Cc: Steve Leyton <[email protected] 
> <mailto:[email protected]>>; Zachary Siegrist 
> <[email protected] <mailto:[email protected]>>
> Subject: RE: standpipe horizontal exit calculation question
>  
> The standard doesn’t really address this condition, but I think it’s 
> consistent with the intent and firefighting strategies that if you have to 
> add a 250 GPM allowance for a standpipe that’s only serving one side of a 
> 2-hour building separation, you would add it to the demand on the valve side 
> of the separation because that is where they’d be coming from.    But 
> ultimately, it might be best to add it to whichever fire area would create 
> the highest demand.    The standard informs that when a single structure is 
> divided into two or more “buildings” by such separations, you have to meet 
> all the demands if they are taken as separate buildings.   So if one area is 
> large enough to require three standpipes, then you’d need to prove 1,000 GPM 
> for that area and lower flows for the others.   
>  
> MY OPINION ONLY.
>  
> Steve Leyton
>  
> From: Sprinklerforum [mailto:[email protected] 
> <mailto:[email protected]>] On Behalf Of Zachary 
> Siegrist via Sprinklerforum
> Sent: Tuesday, January 21, 2020 1:15 PM
> To: [email protected] 
> <mailto:[email protected]>
> Cc: Zachary Siegrist
> Subject: standpipe horizontal exit calculation question
>  
> In a building recognized as part of separate fire areas, the annex material 
> in NFPA 14 Section 7.10.1.1 <http://7.10.1.1/> states the the total supply 
> can be calculated based on the single bldg/ fire area requiring the greatest 
> number of standpipes.  In this scenario, the physical separation between fire 
> areas is functioning as a horizontal exit requiring a hose valves at the 
> horizontal exit.  One side of the wall meets the 100 ft. + 30 ft. hose stream 
> exemption while the other side does not.  The hose valves will be fed via an 
> independent vertical standpipe riser.
> Is this hose valve located at the horizontal exit calculated as part of the 
> area it is located in or calculated as part of the building it serves on the 
> opposite side of the horizontal exit?   I thought this was addressed 
> somewhere in 14 but I can't locate it.
>  
> Can anyone help me out this afternoon?
>  
> Zach
>  
>  
>  
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> <mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to