Per the 2019 edition of NFPA 20:
/4.7.1* Fire pumps shall be dedicated to and listed for fire
protection service.
/
The identical language was contained in the 2013 and 2016 editions.
It would be a good idea to be familiar with the term "listed" as defined
in NFPA 20 [also 2019 edition]:
/3.2.3* Listed. Equipment, materials, or services included in a list
published by an organization that is acceptable to the authority
having jurisdiction and concerned with evaluation of products or
services, that maintains periodic inspection of production of listed
equipment or materials or periodic evaluation of services, and whose
listing states that either the equipment, material, or service meets
approprite designated standards or has been tested and found
suitable //for a specified purpose/.
So, it appears the short answer is "yes."
sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> ***
On 01/23/2020 9:55 AM, Luis Perea via Sprinklerforum wrote:
Hi Everyone
Does The Fire Pump needs to be UL to comply with NFPA 20?
Regards.
[email protected]
Base Firma RSE