FM is acceptable in some cases depending on the AHJ.  Most accept an item if 
it's FM  Approved but I've run into those who did not.  They insisted on a UL 
label.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum <[email protected]> On Behalf 
Of Mike Hairfield via Sprinklerforum
Sent: Thursday, January 23, 2020 1:30 PM
To: [email protected]
Cc: Mike Hairfield <[email protected]>
Subject: [EXTERNAL] Re: Fire Pump NFPA 20

FM Global is acceptable also.

Mike

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Parsley Consulting via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Sent: Thursday, January 23, 2020 1:26 PM
To: Luis Perea via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Cc: Parsley Consulting 
<[email protected]<mailto:[email protected]>>
Subject: Re: Fire Pump NFPA 20

Per the 2019 edition of NFPA 20:
4.7.1* Fire pumps shall be dedicated to and listed for fire protection service.
The identical language was contained in the 2013 and 2016 editions.

It would be a good idea to be familiar with the term "listed" as defined in 
NFPA 20 [also 2019 edition]:
3.2.3* Listed. Equipment, materials, or services included in a list published 
by an organization that is acceptable to the authority having jurisdiction and 
concerned with evaluation of products or services, that maintains periodic 
inspection of production of listed equipment or materials or periodic 
evaluation of services, and whose listing states that either the equipment, 
material, or service meets approprite designated standards or has been tested 
and found suitable for a specified purpose.
So, it appears the short answer is "yes."

sincerely,
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the 
website<https://urldefense.com/v3/__http:/www.parsleyconsulting.com/__;!!B5cixuoO7ltTeg!Rbgr_B67TZS4bzgOK7xpXlikv5xfmK-iEV4tyS4EAeOoCYLXM1yaQiFvNZ8IP8itMA$>
On 01/23/2020 9:55 AM, Luis Perea via Sprinklerforum wrote:

Hi Everyone

Does The Fire Pump needs to be UL to comply with NFPA 20?



Regards.



[[email protected]]

[Base Firma                RSE]





_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!Rbgr_B67TZS4bzgOK7xpXlikv5xfmK-iEV4tyS4EAeOoCYLXM1yaQiFvNZ9IY9htMg$>


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to