Yes, cooking oil is typically a class IIIB combustible. The MAQ has no bearing on the sprinkler design. The density chosen should be based on the hazard present not the building occupancy unless there is specific code language dictating a design criteria as it relates to a very specific building occupancy.
Depending on the quantity (typically anything over 5 gallons), there may be need for this area to be protected by an EHI or EHII system. Look up the definitions for OHI versus EHII regarding flammable and combustible liquids. They shouldn't exist but in small insignificant quantities in an OHI occupancy. Add to the fact that cooking oil is a non-miscible liquid (floats on water, won't mix) and an OHI becomes little more than a building decoration. So first, this a combustible liquid not flammable, there is a distinct difference. It would also be helpful to know what the volume is of what is in use and/or stored and what type of containers is this material in. Then go to NFPA 30 and see where it directs you as far as sprinkler design in the area. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | [email protected] | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Steele, Andrew via Sprinklerforum Sent: Wednesday, February 26, 2020 10:32 AM To: '[email protected]' <[email protected]> Cc: Steele, Andrew <[email protected]> Subject: [EXTERNAL] RE: Flammable liquid tanks in a garage My thoughts - cooking oil is a class IIIB combustible liquid; the model building codes would limit to not more than 13,200 gallons before changing to an H use group. If the containers are metal, then no issue. If they are plastic (prohibited for class I flammables and class II and IIIA combustible liquids), then more consideration should be given to density, particularly if the containers were to remain exposed/unprotected from persons or adjacent vehicles (think car fire exposure, etc.). Andrew Steele -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Sean Lockyer via Sprinklerforum Sent: Wednesday, February 26, 2020 9:38 AM To: Prahl, Craig/GVL; [email protected] Cc: Sean Lockyer Subject: RE: Flammable liquid tanks in a garage Craig, Cooking oils are being stored; per the specs I was provided the tanks meet the requirements of NFPA 30 (2015) and Chapter 19.7 of the 2015 IFC. As for the existing system, the garage was designed for an ordinary group 1 and is protected with a dry system. The initial fear from my service side was that this would require the system to be re-calculated for an extra hazard (and thus, completely reworked based upon the density). My hope is that an enclosure in accordance with NFPA would be sufficient but I am still trying to gather more information before I approach the AHJ. Hope this helps. Thanks for all of the ideas so far... -Sean -----Original Message----- From: Prahl, Craig/GVL <[email protected]> Sent: Wednesday, February 26, 2020 9:21 AM To: [email protected] Cc: Sean Lockyer <[email protected]> Subject: RE: Flammable liquid tanks in a garage What kind of flammable liquid would be used in a restaurant? Liquid propane? And you say the garage area has sprinkler protection? What density? Wet or dry? Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | [email protected] | http://www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Sean Lockyer via Sprinklerforum Sent: Wednesday, February 26, 2020 12:29 AM To: [email protected] Cc: Sean Lockyer <[email protected]>; [email protected] Subject: [EXTERNAL] Flammable liquid tanks in a garage There is a garage with an existing system that has a restaurant on the floor above; the restaurant has (2) exposed flammable liquid tanks in the garage (with piping connected from the restaurant above to the tanks below. Question: What does this do to the hazard classification in the garage ? Would the owner need to built an NFPA 30 type enclosure around the tanks ? A bit of a grey area and not really sure how to proceed. Never seen this before. What says everyone ? Sean Lockyer Project Designer 6817 N. Orange Blossom Trail Cell 386-279-1197 Orlando, Florida 32810 [email protected] Phone: 407-816-9101 https://urldefense.com/v3/__http://www.AITLifeSafety.com__;!!B5cixuoO7ltTeg!WDAPacaDZW3FPOfWQ6RCLZCFQpAiXYPZlGKoRNU1kt2i__WsOxnXPdMFs4jj65Q5wQ$ _______________________________________________ Sprinklerforum mailing list [email protected] https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QIHpVwEkXI3H-6EHVx-DUOsN7fOS8TV-3xeDn8VOukm2Ctiy-Jo_Cn-CsdzalvTnbg$ ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. _______________________________________________ Sprinklerforum mailing list [email protected] https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WDAPacaDZW3FPOfWQ6RCLZCFQpAiXYPZlGKoRNU1kt2i__WsOxnXPdMFs4g_kY4O6w$ _______________________________________________ Sprinklerforum mailing list [email protected] https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WDAPacaDZW3FPOfWQ6RCLZCFQpAiXYPZlGKoRNU1kt2i__WsOxnXPdMFs4g_kY4O6w$ ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org