Residential use above a parking garage changes the occupancy requirement to
a mixed use and NFPA 13 design criteria is required. Therefore protect the
garage. Am I on the right track here?

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Irwin via Sprinklerforum
Sent: Friday, May 29, 2020 5:55 AM
To: [email protected]
Cc: John Irwin
Subject: Covered Parking in 13R

 

I have a 3-story, 13R building. Type IIB construction. On the "engineered"
bid set, no sprinklers are shown in the covered parking area. This area is
inside the footprint of the first floor, with 2nd floor units being located
above the parking area. There are no garage doors and the parking spaces are
not separated. To sprinkle or not to sprinkle?

 

 

 