I have an odd situation that I haven't come across before.  We requested a
water test and received a water test from the fire department for a project
that incorporated a private hydrant.  The test was performed on the private
hydrant but since there was only a single hydrant on the private side of
the water supply, the fire department placed the static and residual gauge
on the #4 test cock on the discharge of the containment backflow
preventer.  I don't see an issue with this, but it was flagged in plan
review and the plans were rejected based on the fact that the test was not
done in an approved manner, since NFPA 291 never references using any other
outlet for a static/residual reading.
Has anyone worked through this, or possibly have a reference I can point
the plan reviewer to other than the obvious "it's just static and residual"?

Thanks Forumites...