If I were allowed to ask such questions (we remember you, George), I'd start
by asking myself what the likelihood the hose stations will actually be used
and for what purpose for that particular project.  Trained personnel other
than the fire department can use them for 1st response, and fire fighters
can use them for mop-up operations.  For 1st response, I can't believe it
would matter what system they are attached to if properly calculated.  For
mop-up, I would agree with you.  If located at the boundary between two
overhead zones and connected to one of those zones, there's a 50% chance it
will be out-of-service if a fire occurred beneath one of those 2 zones.

Ed K

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Tony Silva via Sprinklerforum
Sent: Saturday, September 26, 2020 3:55 PM
To: [email protected]
Cc: Tony Silva <[email protected]>
Subject: Small Hose Stations

In a storage occupancy that requires small hose stations complying with NFPA
13, an acceptable method of connection is to supply from an "Adjacent
Sprinkler System". Some hose stations fall right in the boundary between two
zones. The contractor wants to supply these hose stations from either one of
these adjacent zones. I am of the opinion that these hose stations should be
supplied from a zone that is not serviced by these hose stations, requiring
longer supply piping.

Any thoughts? What is your position on this issue?

Thanks,

Tony
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to