Blazemaster has very specific criteria for this:
"When the piping is supported by wood joists or trusses by laying the pipe
directly on top of 
the structural members, the structure provides the support, assuming that
the center spacing 
of the structural member does not exceed the requirements of Table Q."

This would include when passing through holes in TJI type joist.

Thank you,

Bob Knight, CET III
Fire by Knight, LLC
208-318-3057

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mike Hairfield via Sprinklerforum
Sent: Wednesday, September 30, 2020 6:39 AM
To: Sprinkler Forum
Cc: Mike Hairfield
Subject: Hangers for CPVC Pipe going through TGI Joists 

The TGI Joists are spaced 16" apart, does NFPA-13 require hangers on the
CPVC pipe since
the TGI joists are supporting the pipe?

Mike