Some of you guys mentioned bushings or "other method to prevent chafing". Can 
we elaborate on that? I've seen bushings used where CPVC is run in a wall and 
passes through metal studs, but I don't think I've seem them installed in this 
scenario. Is that really a requirement?

-Kyle M

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Bob Knight via Sprinklerforum
Sent: Wednesday, September 30, 2020 7:34 AM
To: [email protected]
Cc: Bob Knight <[email protected]>
Subject: [EXTERNAL] RE: Hangers for CPVC Pipe going through TGI Joists 

Blazemaster has very specific criteria for this:
"When the piping is supported by wood joists or trusses by laying the pipe 
directly on top of the structural members, the structure provides the support, 
assuming that the center spacing of the structural member does not exceed the 
requirements of Table Q."

This would include when passing through holes in TJI type joist.

Thank you,

Bob Knight, CET III
Fire by Knight, LLC
208-318-3057

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mike Hairfield via Sprinklerforum
Sent: Wednesday, September 30, 2020 6:39 AM
To: Sprinkler Forum
Cc: Mike Hairfield
Subject: Hangers for CPVC Pipe going through TGI Joists 

The TGI Joists are spaced 16" apart, does NFPA-13 require hangers on the CPVC 
pipe since the TGI joists are supporting the pipe?

Mike
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=SdpFbtMK1-jneilmi9UX9Wb03ucgatk8Er3sXcgCh6E&s=XYdJw3dIVQhLU9W8Ze4bpJwVi6BXWr9cAP4hS626p50&e=
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=SdpFbtMK1-jneilmi9UX9Wb03ucgatk8Er3sXcgCh6E&s=XYdJw3dIVQhLU9W8Ze4bpJwVi6BXWr9cAP4hS626p50&e=
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to