We have a project that was pre-engineered.  It has several issues that we are 
having to correct.  One is something I haven’t considered.  We have a concealed 
combustible space that requires 130 sq ft max spacing.  The pendents are 225 sq 
ft max spacing.  All of the walls for the office spaces – think medical office 
type project – are full height to deck and drywalled.  Is there any reason you 
wouldn’t use the small room method for determining area per sprinkler for the 
SSU in the concealed space?
 
For example, the room may be 120 sq ft for example.  However, the SSU located 
by the FPE is 6’ off the north wall and 6’ off the west wall.  Using SxL, this 
would be 144 sq ft per sprinkler.  But, if the space above the ceiling could be 
treated as a small room, then the area per sprinkler could be the room area 
divided by the number of sprinklers in the room.  This would mean the sprinkler 
is 120 sq ft per sprinkler.
 
This happens in several places.  There are many instances where I can just move 
the sprinkler to be more centered and solve the problem, but not all areas.  
So, would you consider that space above the ceiling to be allowed to follow 
small room rules?



Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
[email protected]
www.mfpdesign.com

Send large files to us via: https://www.hightail.com/u/MFPDesign 
LinkedIn: https://www.linkedin.com/in/travismack

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with ferguson.com, click here to 
register.*
**Have a Ferguson account? Download the Ferguson app for on-the-go access to 
your favorite ferguson.com features. Apple iOS devices or Android devices**

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to