Are you required to use concealed space sprinklers?   
  

  
If it meets the NFPA definition of a room and the requirements of 11.2.3.3 are 
met, then you should be able to use it above a ceiling. Be sure of any fire 
resistance rating requirements.
  
  
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Oct 7, 2020 at 7:59 PM,  <Travis Mack via Sprinklerforum 
> (mailto:[email protected])>  wrote:
>   
>   
>   
>  We have a project that was pre-engineered. It has several issues that we are 
> having to correct. One is something I haven’t considered. We have a concealed 
> combustible space that requires 130 sq ft max spacing. The pendents are 225 
> sq ft max spacing. All of the walls for the office spaces – think medical 
> office type project – are full height to deck and drywalled. Is there any 
> reason you wouldn’t use the small room method for determining area per 
> sprinkler for the SSU in the concealed space? For example, the room may be 
> 120 sq ft for example. However, the SSU located by the FPE is 6’ off the 
> north wall and 6’ off the west wall. Using SxL, this would be 144 sq ft per 
> sprinkler. But, if the space above the ceiling could be treated as a small 
> room, then the area per sprinkler could be the room area divided by the 
> number of sprinklers in the room. This would mean the sprinkler is 120 sq ft 
> per sprinkler. This happens in several places. There are many instances where 
> I can just move the sprinkler to be more centered and solve the problem, but 
> not all areas. So, would you consider that space above the ceiling to be 
> allowed to follow small room rules? Travis Mack, CFPS, CWBSP, RME-G, SET 
> Engineering Manager MFP Design 3356 E Vallejo Ct Gilbert, AZ 85298 NEW 
> EXTENSION: 480-505-9271 ext. 700 NEW MOBILE: 480-272-2471 
> [email protected] www.mfpdesign.com Send large files to us via: 
> https://www.hightail.com/u/MFPDesign LinkedIn: 
> https://www.linkedin.com/in/travismack “The bitterness of poor quality 
> remains long after the sweetness of low price is forgotten.” Need/Want a 
> faster way to check material pricing? Build a material quote? Check 
> availability ? Searching for an invoice? *If you do not already have an 
> account with ferguson.com, click here to register.* **Have a Ferguson 
> account? Download the Ferguson app for on-the-go access to your favorite 
> ferguson.com features. Apple iOS devices or Android devices** 
> _______________________________________________ Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org  
>
>   
  
  
     
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to