You first start with the Fire Code adopted in the community. The fire code has requirements for flammable and combustible liquids and also includes fire protection requirements. You have to start there. The IFC varies from NFPA 30 in some sections. There are maximum allowable quantities (MAQ's) and other requirements.
Scott Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -----Original Message----- From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Thursday, November 5, 2020 2:29 PM To: sprinklerforum@lists.firesprinkler.org Cc: Prahl, Craig/GVL <craig.pr...@jacobs.com>; Fpdcdesign <fpdcdes...@gmail.com> Subject: RE: [EXTERNAL] Re: Class IA Flammable Liquids 1A materials are fairly uncommon. Often they are mislabeled due to people only looking at the flash point and not at the boiling point of the liquid. In cosmetics 1B is common. You need to know exactly what the material is. Request a SDS on the material. NFPA doesn't get into comparing quantities to sprinkler design. You need to know what it is, how much there is, what kind of container is it in, is it just stored or is there any dispensing of the product, is it stored on the floor or on racks. What does the SDS indicate as far as approved firefighting methods. Do these areas handling the 1B and potentially 1A have secondary containment of the spilled material within the room (pool fire) or is it evacuated out of the area? Those are the opening questions. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 > I'm confused about how to treat Class IA flammable liquids. We've got a > cosmetics manufacturer that is moving into a shell building. They are > planning a Hazardous Storage room to store the flammable liquids when not in > use. The liquids being stored are primarily Class IB solvents, but I'm being > told there is "some amount" of Class IA liquids (I think a relatively small > amount, but they haven't given me the quantities yet). I'm confused because > the protection criteria in NFPA 30 chapter 16 specifically notes that it > doesn't apply to Class IA liquids. If we design the fire protection for that > room for Class IB liquids, is there a certain maximum allowable quantity of > Class IA that they can store in there and still be considered protected? I > feel like there is an obvious answer here, but I must be looking right past > it. Thanks for the help. -Kyle M > _______________________________________________ Sprinklerforum mailing list ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org