If they have adopted the IFC. First go to the flammable liquid chapter 57. This 
will send you to chapter 50 for hazardous materials. This will give you MAQ. 
Consult the tables. Is building sprinklered. Mr. Prahl is correct. Find out 
what, where, and quantity.

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Kyle.Montgomery via Sprinklerforum
Sent: Thursday, November 5, 2020 12:11 PM
To: [email protected]
Cc: Kyle.Montgomery <[email protected]>
Subject: Class IA Flammable Liquids

I'm confused about how to treat Class IA flammable liquids. We've got a 
cosmetics manufacturer that is moving into a shell building. They are planning 
a Hazardous Storage room to store the flammable liquids when not in use. The 
liquids being stored are primarily Class IB solvents, but I'm being told there 
is "some amount" of Class IA liquids (I think a relatively small amount, but 
they haven't given me the quantities yet).

I'm confused because the protection criteria in NFPA 30 chapter 16 specifically 
notes that it doesn't apply to Class IA liquids. If we design the fire 
protection for that room for Class IB liquids, is there a certain maximum 
allowable quantity of Class IA that they can store in there and still be 
considered protected? I feel like there is an obvious answer here, but I must 
be looking right past it.

Thanks for the help.

-Kyle M
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
[NOTICE: This message originated from an external source -- DO NOT CLICK on 
links or open attachments unless you are sure the content is safe.]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to