You need to look at the type and quantity of fuel and LP storage in RV and 
motor fuel type and quantity in the boats being stored. For boat storage it is 
common to store boats with their internal fuel tanks full, with the boats being 
considered as plastic composite construction. You might need to consider an 
larger remote area of sprinkler operation because of the shielded areas in the 
RVs and boats which delays the operation of sprinklers until the fire burns 
through the construction shielding the fire from the sprinkler system. When the 
fire breaches the construction containing the fire the heat release is great 
with the possibility of operating sprinkler heads beyond the normal 2,000 or 
3,000 sq ft remote area. When you look at manufacturers of mobile homes you 
will find sprinkler systems designed with remote areas of 5,000 sq ft to 
address the significant heat release of the shielded fire burning through the 
non-sprinklered mobile home (not much different than an RV or boat with cabin, 
however RV and boat have fuel tanks and fuel storage). 

Have a fire safe and healthy day!

Jim Davidson      

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Prahl, Craig/GVL via Sprinklerforum
Sent: January 11, 2021 8:44 AM
To: [email protected]
Cc: Prahl, Craig/GVL <[email protected]>; John Paulsen <[email protected]>
Subject: RE: RV Storage

I concur.

RVs represent a concealed hazard, boats not so much unless they are larger with 
cabins. Then consider the proximity of one unit to another.  Any fire is going 
to involve several units.  Even EH2 would probably be like spitting on a forest 
fire.

Building  height also plays a role. The other questions, are there any 
smoke/heat vents in the building?  What kind of square footage of space is 
available for RV storage?

What's the local water supply like?

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
[email protected] | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of John Paulsen via Sprinklerforum
Sent: Friday, January 8, 2021 5:12 PM
To: [email protected]
Cc: John Paulsen <[email protected]>
Subject: [EXTERNAL] RE: RV Storage

Guys,

If you don't own a boat or RV, it's hard to imagine the fire load these units 
can represent. Campers especially pose the situation of an internal fire 
becoming well developed before it breaks through the roof and the sprinklers 
get a chance to attack it. Oh, and don't forget to add in the explosion hazard 
of the propane tanks most campers have. Runabouts, waverunners and cruisers all 
have the potential to have large amount of plastics, gasoline and lubricants on 
board. I've personally stored boats for the winter inside a building with 80 
gallons of 100 octane gas in the tank and there were 30 other boats of various 
sizes right next to mine with the same or greater fuel capacity. Some storage 
venues ask that you drain your tanks before you bring it in, but I have never 
seen anyone check for compliance.

Some of the recent marina fires that have occurred in Alabama and Michigan show 
how devastating a fire can be in situations with multiple boats and RV's stored 
under the same roof.

EH II at a minimum gives the best chance of saving at least part of the 
building and a high K factor CMHD or ESFR head would not be out of the question.

MHO,

John Paulsen – SET
Sprinkler System Design & Sales
Silco Fire and Security
2345 Southwest Blvd.
Grove City, OH 43123
P-614-449-2101 Ext. 3367
F-614-449-2007
C-614-348-8206




-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of John Denhardt via Sprinklerforum
Sent: Friday, January 8, 2021 4:48 PM
To: [email protected]
Cc: John Denhardt <[email protected]>
Subject: Re: RV Storage

My suggestions:


   - RV Storage Building* - Extra Hazard Group 2*
   - Boat Storage Building (just parked, not on racks) *- Extra Hazard
   Group 2*
   - Storage lockers with height less than 12 feet *- Depends on what is
   being stored.  For example, Group A plastics might be more demanding.
   Follow miscellaneous storage chart in NFPA 13.*

Hope this helps

*The above is my personal opinion as a professional engineer.  It has not been 
processed as a formal interpretation in accordance with the NFPA Regulations 
Governing Committee Projects and should therefore not be considered, nor relied 
upon, as the official position of the NFPA.*

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://urldefense.com/v3/__https://www.facebook.com/firesprinkler.org/__;!!B5cixuoO7ltTeg!S5I3gLWZH8aL-fnCDaYS3BvyKmmfQp-_ab1_Y8mwOMqaAppuwc8by4f4AxWn4amWmA$
 > 
<https://urldefense.com/v3/__https://twitter.com/afsa/status/1039528345367732224__;!!B5cixuoO7ltTeg!S5I3gLWZH8aL-fnCDaYS3BvyKmmfQp-_ab1_Y8mwOMqaAppuwc8by4f4AxWavZbiNQ$
 > 
<https://urldefense.com/v3/__https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/__;!!B5cixuoO7ltTeg!S5I3gLWZH8aL-fnCDaYS3BvyKmmfQp-_ab1_Y8mwOMqaAppuwc8by4f4AxVwtD4f2Q$
 >
   
<https://urldefense.com/v3/__https://www.instagram.com/firesprinklerorg/__;!!B5cixuoO7ltTeg!S5I3gLWZH8aL-fnCDaYS3BvyKmmfQp-_ab1_Y8mwOMqaAppuwc8by4f4AxVauiRivQ$
 >

*Our members are at the heart of everything we do.*

*Love free stuff? *

Tell an industry friend why you are an AFSA member and when they join or 
re-join the AFSA family, you will receive a $100 Amazon gift card and they’ll 
receive one free AFSA on-demand webinar of their choice—including CEUs (a $250 
value)! It’s our way to say thank you and welcome. Offer valid through December 
31, 2020. Visit firesprinkler.org/join 
<https://urldefense.com/v3/__https://www.firesprinkler.org/WWW/Membership/Membership_Home_2.aspx?hkey=aaf9ae7c-5cf9-4981-b8f5-d852a5de39c5&WebsiteKey=3dff22a3-0306-479c-bccc-7aa1986c8ada__;!!B5cixuoO7ltTeg!S5I3gLWZH8aL-fnCDaYS3BvyKmmfQp-_ab1_Y8mwOMqaAppuwc8by4f4AxWW7SG83Q$
 > .


On Fri, Jan 8, 2021 at 3:29 PM Kyle.Montgomery via Sprinklerforum < 
[email protected]> wrote:

> Certainly EH 2 seems like it will get the job done. But for those of 
> you saying that, which commodity drives you to that? For example, if 
> they were three separate buildings:
>
> RV Storage Building
> Boat Storage Building (just parked, not on racks) Storage lockers with 
> height less than 12 feet
>
> Would you consider each of those EH 2 on their own? Or would one or 
> more of those be a lesser hazard?
>
> -Kyle M
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]>
> On Behalf Of Steve Leyton via Sprinklerforum
> Sent: Friday, January 8, 2021 9:27 AM
> To: [email protected]
> Cc: Steve Leyton <[email protected]>
> Subject: [EXTERNAL] RE: RV Storage
>
> Concur.  We have done a couple previously that were takeovers with 
> CMDA sprinklers and have one currently in progress that used to be a Lowe's
> store and is protected with ESFR.   EH2 by the book (IMHO), but we had one
> AHJ who insisted on .45/2000 (he had his reasons).
>
> Steve Leyton
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Byron 
> Weisz via Sprinklerforum
> Sent: Friday, January 08, 2021 8:16 AM
> To: [email protected]
> Cc: Byron Weisz <[email protected]>
> Subject: RE: RV Storage
>
> Multiple Projects - Extra Hazard Group II
>
>
> Byron Weisz
>
> Cen-Cal Fire Systems, Inc.
> P.O. Box 1284
> Lodi,  CA   95241
> Phone (209)  334-9119
> Fax      (209)  334-2923
> [email protected]
>
> This and any attached documents are for the use of the intended
> recipient(s) only and may contain information that is privileged, 
> confidential, or work product that may be exempt from disclosure under 
> applicable law. If you are not the intended recipient, any use, 
> dissemination, distribution, or copying of this communication and any 
> attachments is strictly prohibited, and you are hereby requested to 
> delete this message and any attached documents, to destroy any printed 
> copies, and to telephone or otherwise contact the sender immediately about 
> the error.
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]>
> On Behalf Of Bobby Welch via Sprinklerforum
> Sent: Friday, January 08, 2021 8:08 AM
> To: [email protected]
> Cc: Bobby Welch <[email protected]>
> Subject: RV Storage
>
> We have a customer who has an existing warehouse with an existing wet 
> system. He is wanting to store RV's and boats in the high bays, and 
> have caged storage lockers in lower areas.
> We are trying to figure out the extent of system upgrades we have to 
> make for the system to work. Storage height will not exceed 12'. We 
> thought this would be close in line with a parking garage facility, 
> but the storage aspect throws it into a gray area considering NFPA has 
> no specific literature referring to this type of storage (besides storage 
> lockers).
> My question is, does anyone have experience designing systems for this 
> type of storage, and if so what were your conclusions? Any advice 
> would help.
> Thanks.
>
> Bobby Welch | Sprinkler Systems Designer KOORSEN FIRE & SECURITY
> 3577 Concorde Rd, Vandalia, OH 45377
> P 937.641.8403 | Ext. 0318 | M 937.594.8457 
> [email protected]<mailto:[email protected]> | 
> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.koorsen.com&d=
> DwIFAw&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8O
> BJwQd9A&m=Nn9EdX7szVASjuM_LZBJiRH_-PaIlhXIQ47pBKjBb24&s=XS6lHFHssW9xwu
> hS9ymqcP43hjmu-iIBQj6qIRJ6Stk&e=
> <
> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.koorsen.com&d=
> DwIFAw&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8O
> BJwQd9A&m=Nn9EdX7szVASjuM_LZBJiRH_-PaIlhXIQ47pBKjBb24&s=XS6lHFHssW9xwu
> hS9ymqcP43hjmu-iIBQj6qIRJ6Stk&e=
> >           .
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle
> r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=wn3mZ
> QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Nn9E
> dX7szVASjuM_LZBJiRH_-PaIlhXIQ47pBKjBb24&s=F-dSsdT1EpjCvLtGyOuwPotPs7_y
> CeA3WtN8Lsp3Lec&e= _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle
> r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=wn3mZ
> QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Nn9E
> dX7szVASjuM_LZBJiRH_-PaIlhXIQ47pBKjBb24&s=F-dSsdT1EpjCvLtGyOuwPotPs7_y
> CeA3WtN8Lsp3Lec&e= _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle
> r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=wn3mZ
> QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Nn9E
> dX7szVASjuM_LZBJiRH_-PaIlhXIQ47pBKjBb24&s=F-dSsdT1EpjCvLtGyOuwPotPs7_y
> CeA3WtN8Lsp3Lec&e= _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cg
> i/sprinklerforum-firesprinkl__;!!B5cixuoO7ltTeg!S5I3gLWZH8aL-fnCDaYS3B
> vyKmmfQp-_ab1_Y8mwOMqaAppuwc8by4f4AxW8M9zpOA$
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!S5I3gLWZH8aL-fnCDaYS3BvyKmmfQp-_ab1_Y8mwOMqaAppuwc8by4f4AxUHTWeq3Q$
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!S5I3gLWZH8aL-fnCDaYS3BvyKmmfQp-_ab1_Y8mwOMqaAppuwc8by4f4AxUHTWeq3Q$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to