My thoughts exactly, Mr Prahl.   
  
  
  
    
  

  
  
>   
> On Feb 11, 2021 at 3:46 PM,  <Craig/GVL via Sprinklerforum Prahl 
> (mailto:[email protected])>  wrote:
>   
>   
>   
>  If I have 4-heads of OH2 in a 500 sf space I have to calc it and size 
> everything as if I had a 1500 sf design area. Where’s the value? What greater 
> level of Life Safety is provided? You should only have to calculate the 
> actual area up to the prescribed area and not add some fictitious value, 
> “just because”. Maybe we should just design everything using ESFR sprinklers, 
> then you’d get all the flow you need. Craig Prahl | Jacobs | Group Lead/SME – 
> Fire Protection |  [email protected] 
> (mailto:[email protected])<mailto:[email protected]>  |  
> www.jacobs.com (http://www.jacobs.com)<http://www.jacobs.com/>   1041 East 
> Butler Road Greenville, South Carolina 29606 (x-apple-data-detectors://6)  
> CONTACT BY: email or MS TEAMS From:  [email protected] 
> (mailto:[email protected])   <[email protected] 
> (mailto:[email protected])>  Sent: Thursday, February 11, 2021 3:22 
> PM To:  [email protected] 
> (mailto:[email protected]);  [email protected] 
> (mailto:[email protected])  Cc: Prahl, Craig/GVL  <[email protected] 
> (mailto:[email protected])>  Subject: RE: [EXTERNAL] RE: Multiple System 
> Calculation Tracey Bellamy, I believe, was the one to propose it. It had to 
> deal with a loading dock and then having to grab ESFR sprinklers in the 
> warehouse to get the 1950 sq ft if I recall correctly. I read the report a 
> couple years ago. I see where he was coming from. The intent was good. But, I 
> think there are a lot of unintended consequences from that section. Travis 
> Mack, CFPS, CWBSP, RME-G, COC, SET Engineering Manager MFP Design  3356 E 
> Vallejo Ct Gilbert, AZ 85298 (x-apple-data-detectors://15/0)   480-505-9271 
> ext. 700 (tel:480-505-9271;700)  C:  480-272-2471 (tel:480-272-2471)   
> [email protected] 
> (mailto:[email protected])<mailto:[email protected]>   
> www.mfpdesign.com 
> (http://www.mfpdesign.com)<https://urldefense.com/v3/__http:/www.mfpdesign.com__;!!B5cixuoO7ltTeg!TvpoXWQR2VWz0zxhIEqEFsTPN06eLs2sEswTD03UHaGwK-R8wwW4QPVZv6MBHNsLBA$>
>   Send large files to us via:  
> https://www.hightail.com/u/MFPDesign<https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D&reserved=0__;JSUlJSUlJSUlJSUlJSU!!B5cixuoO7ltTeg!TvpoXWQR2VWz0zxhIEqEFsTPN06eLs2sEswTD03UHaGwK-R8wwW4QPVZv6OcFBfotw$>
>  
> (https://www.hightail.com/u/MFPDesign%3Chttps://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D&reserved=0__;JSUlJSUlJSUlJSUlJSU!!B5cixuoO7ltTeg!TvpoXWQR2VWz0zxhIEqEFsTPN06eLs2sEswTD03UHaGwK-R8wwW4QPVZv6OcFBfotw$%3E)
>   From: Sprinklerforum  <[email protected] 
> (mailto:[email protected])<mailto:[email protected]>>
>   On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Thursday, February 
> 11, 2021 1:20 PM To:  [email protected] 
> (mailto:[email protected])<mailto:[email protected]>;  
> [email protected] 
> (mailto:[email protected])<mailto:[email protected]>
>   Cc: Prahl, Craig/GVL  <[email protected] 
> (mailto:[email protected])<mailto:[email protected]>>  Subject: RE: 
> [EXTERNAL] RE: Multiple System Calculation This is something that really 
> needs to be looked at I future editions of NFPA 13. I know we've had this 
> discussion many times. I would love to hear how this came about. It offers no 
> benefit to an owner and only increases cost. Craig Prahl | Jacobs | Group 
> Lead/SME – Fire Protection |  [email protected] 
> (mailto:[email protected])<mailto:[email protected]>  |  
> www.jacobs.com (http://www.jacobs.com)<http://www.jacobs.com>   1041 East 
> Butler Road Greenville, South Carolina 29606 (x-apple-data-detectors://34)  
> CONTACT BY: email or MS TEAMS -----Original Message----- From: Sprinklerforum 
>  <[email protected] 
> (mailto:[email protected])<mailto:[email protected]>>
>   On Behalf Of Bob Knight via Sprinklerforum Sent: Thursday, February 11, 
> 2021 2:24 PM To:  [email protected] 
> (mailto:[email protected])<mailto:[email protected]>
>   Cc: Bob Knight  <[email protected] 
> (mailto:[email protected])<mailto:[email protected]>>  Subject: 
> [EXTERNAL] RE: Multiple System Calculation Joe, The AHJ's interpretation 
> sounds incorrect. What is supposed to take place is as follows: 23.4.4.2.5 
> Where the total design discharge from these operating sprinklers is less than 
> the minimum required discharge determined by multiplying the required design 
> density times the required minimum design area, an additional flow shall be 
> added at the point of connection of the branch line to the cross main 
> furthest from the source to increase the overall demand, not including hose 
> stream allowance, to the minimum required discharge. In other words, we are 
> now required to add additional flow to calculations when we are in a 
> situation like yours. The minimum required flow for a 1500 sf design area for 
> OH1 is 210 gpm, and the minimum required flow For 1950 sf is 292.5 gpm. If 
> your areas are not flowing these minimus you will need to add the additional 
> flow as stated above. It's a pain in the neck but other than one more step in 
> the calc that's it. Thank you, Bob Knight, CET III Fire by Knight, LLC  
> 208-318-3057 (tel:208-318-3057)  -----Original Message----- From: 
> Sprinklerforum [mailto:[email protected]] On 
> Behalf Of Joe Burtell via Sprinklerforum Sent: Thursday, February 11, 2021 
> 11:47 AM To:  [email protected] 
> (mailto:[email protected])<mailto:[email protected]>
>   Cc: Joe Burtell Subject: Multiple System Calculation I have a situation 
> where an engineer is telling me I have to calculate a wet and dry system 
> together because neither space meets the 1500 s.f minimum. I have a penthouse 
> mechanical room OH 1 (WET) of 1014 s.f. and an adjacent room OH1 (DRY) of 469 
> s.f. I have calculated each room separate of each other. There is a 
> full-height wall with a door that separates the rooms. The wall and door are 
> not fire rated, so the large room method is out. This does not make any sense 
> to me. Any sections that would require this to be done. He is saying 11.1.2 
> of NFPA 13 2016 requires it. I argue exception #2 says it does not apply. 
> Best regards, *Joe Burtell, SET, CFPS* [image: Burtell Fire_Small] Phone | 
> Fax | Mobile| Text *406-204-4653 (tel:406-204-4653)   <++1-406-204-4653>*  
> 116 N. 11th Street | Billings, MT 59101 (x-apple-data-detectors://50/1)  
> Email:  [email protected] 
> (mailto:[email protected])<mailto:[email protected]>  Web Site:  
> https://urldefense.com/v3/__http://www.burtellfire.com__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhXpTjY7tQ$<https://urldefense.com/v3/__http:/www.burtellfire.com__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhXpTjY7tQ$>
>  
> (https://urldefense.com/v3/__http://www.burtellfire.com__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhXpTjY7tQ$%3Chttps://urldefense.com/v3/__http:/www.burtellfire.com__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhXpTjY7tQ$%3E)
>   *“**The bitterness of poor quality remains long after the sweetness of low 
> price is forgotten.**”* *NOTICE:* The information contained in this e-mail 
> transmission is intended only for use of the individual or entity named 
> above. This e-mail transmission, and any documents, files, previous e-mail 
> transmissions or other information attached to it, may contain confidential 
> information that is legally privileged. If you are not the intended recipient 
> of this e-mail transmission, or the employee or agent responsible for 
> delivering it to the intended recipient, you are hereby notified that any 
> disclosure, dissemination, distribution, copying or other use of this 
> transmission or any of the information contained in or attached to this 
> e-mail is strictly prohibited. If you have received this e-mail transmission 
> in error, please immediately notify us by return e-mail transmission and 
> destroy the original e-mail transmission as well as its attachments without 
> reading or saving it in any manner. Thank you. 
> _______________________________________________ Sprinklerforum mailing list  
> [email protected] 
> (mailto:[email protected])<mailto:[email protected]>
>    
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhUWL4WtCw$<https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhUWL4WtCw$>
>  
> (https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhUWL4WtCw$%3Chttps://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhUWL4WtCw$%3E)
>   _______________________________________________ Sprinklerforum mailing list 
>  [email protected] 
> (mailto:[email protected])<mailto:[email protected]>
>    
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhUWL4WtCw$<https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhUWL4WtCw$>
>  
> (https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhUWL4WtCw$%3Chttps://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QcpRmtH3H4A1gC3M5IjCfS8-2CaVFcLWuBfbZeFBrhOG0NXLokjsdc5NxhUWL4WtCw$%3E)
>   ________________________________ NOTICE - This communication may contain 
> confidential and privileged information that is for the sole use of the 
> intended recipient. Any viewing, copying or distribution of, or reliance on 
> this message by unintended recipients is strictly prohibited. If you have 
> received this message in error, please notify us immediately by replying to 
> the message and deleting it from your computer. 
> _______________________________________________ Sprinklerforum mailing list  
> [email protected] 
> (mailto:[email protected])<mailto:[email protected]>
>    
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!TvpoXWQR2VWz0zxhIEqEFsTPN06eLs2sEswTD03UHaGwK-R8wwW4QPVZv6NoFrqsww$>
>  
> (http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org%3Chttps://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!TvpoXWQR2VWz0zxhIEqEFsTPN06eLs2sEswTD03UHaGwK-R8wwW4QPVZv6NoFrqsww$%3E)
>   ________________________________ NOTICE - This communication may contain 
> confidential and privileged information that is for the sole use of the 
> intended recipient. Any viewing, copying or distribution of, or reliance on 
> this message by unintended recipients is strictly prohibited. If you have 
> received this message in error, please notify us immediately by replying to 
> the message and deleting it from your computer. 
> _______________________________________________ Sprinklerforum mailing list  
> [email protected] 
> (mailto:[email protected])   
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org  
>  
>
>   
  
  
     