All - For the 2022 edition of NFPA 13, some clarifications and changes are
coming for the "Phantom Flow" calculation process.  The diagram in the
annex has been revised.  These changes are still tentative since the NITIAM
process is currently occurring. Hopefully, these changes will make it
easier to understand.  NFPA's website has the proposed language.

*The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the AFSA, NFPA, or NFPA's technical
committees. AFSA cannot provide design or consulting engineering services,
and this opinion should therefore not be considered, nor relied upon, as
such.*

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do*


*Be a Member, Get a Member*

We’re introducing many new programs to help meet your team’s business
needs. AFSA is offering a six-month trial membership for contractors and a
12-month trial membership for municipal AHJs. Let’s help potential members
see what they’re missing! Current members who recruit a new contractor
member will receive a $100 gift card and the new member gets a free
webinar.  Let’s grow stronger together! Join AFSA
<http://www.firesprinkler.org/join>.




On Fri, Feb 12, 2021 at 2:00 PM Sean Conlin via Sprinklerforum <
[email protected]> wrote:

> See NFPA-13, 23.4.4.1.1.4 and 23.4.4.1.1.5.
>
>
>
> This should help you with the engineer.
>
>
> Regards,
>
> Sean W. Conlin, A.Sc.T.
> Director
> Demand Sprinkler Design Inc.
> 37 Summerfield Crescent
> Brampton, ON L6X 4K4
> T: 905-216-0922
> C: 416-317-0028
> E: [email protected]
>
> This message, including any attachments is considered confidential and for
> use only by the intended recipient(s).
> Any other distribution, copying or disclosure is strictly prohibited.
> Please delete this communication and notify
> Demand Sprinkler Design Inc. if you are not the intended recipient or have
> received this message in error. Demand
> Sprinkler Design Inc. accepts no responsibility or liability for any loss
> or damage from use, including damage from viruses.
>
>
>
> -----Original Message-----
> From: Joe Burtell <[email protected]>
> Sent: February 11, 2021 1:47 PM
> To: [email protected]
> Subject: Multiple System Calculation
>
>
>
> I have a situation where an engineer is telling me I have to calculate a
> wet and dry system together because neither space meets the 1500 s.f
> minimum. I have a penthouse mechanical room OH 1 (WET) of 1014 s.f. and an
> adjacent room OH1 (DRY) of 469 s.f. I have calculated each room separate of
> each other. There is a full-height wall with a door that separates the
> rooms. The wall and door are not fire rated, so the large room method is
> out. This does not make any sense to me. Any sections that would require
> this to be done. He is saying 11.1.2 of NFPA 13 2016 requires it. I argue
> exception #2 says it does not apply.
>
>
>
> Best regards,
>
>
>
> *Joe Burtell, SET, CFPS*
>
>
>
> [image: Burtell Fire_Small]
>
>
>
> Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
>
>
>
> 116 N. 11th Street | Billings, MT 59101
>
>
>
> Email: [email protected]<mailto:[email protected]>
>
>
>
> Web Site: http://www.burtellfire.com
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of low
> price is forgotten.**”*
>
>
>
> *NOTICE:*  The information contained in this e-mail transmission is
> intended only for use of the individual or entity named above.  This e-mail
> transmission, and any documents, files, previous e-mail transmissions or
> other information attached to it, may contain confidential information that
> is legally privileged.  If you are not the intended recipient of this
> e-mail transmission, or the employee or agent responsible for delivering it
> to the intended recipient, you are hereby notified that any disclosure,
> dissemination, distribution, copying or other use of this transmission or
> any of the information contained in or attached to this e-mail is strictly
> prohibited.  If you have received this e-mail transmission in error, please
> immediately notify us by return e-mail transmission and destroy the
> original e-mail transmission as well as its attachments without reading or
> saving it in any manner.  Thank you.
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to