No, I have not seen the drawing.

Dane - please send me the drawing.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do*


*Be a Member, Get a Member*

We’re introducing many new programs to help meet your team’s business
needs. AFSA is offering a six-month trial membership for contractors and a
12-month trial membership for municipal AHJs. Let’s help potential members
see what they’re missing! Current members who recruit a new contractor
member will receive a $100 gift card and the new member gets a free
webinar.  Let’s grow stronger together! Join AFSA
<http://www.firesprinkler.org/join>.




On Mon, Feb 15, 2021 at 11:03 AM Kyle.Montgomery <[email protected]>
wrote:

> Have you guys had a chance to look at the actual plans Dane is dealing
> with? It seems to meet the letter of the law for not requiring additional
> heads, but it also looks like the outlier that the committee probably
> wasn't expecting when that was written. In plan view, these panels cover
> nearly 90% of the floor area. I'm not saying that you definitely need
> sprinklers, but it would be cool to see some fire modeling or something to
> see the impact of these panels on activation time and/or sprinkler
> discharge.
>
> -Kyle M
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of John Denhardt via Sprinklerforum
> Sent: Monday, February 15, 2021 8:48 AM
> To: [email protected]
> Cc: John Denhardt <[email protected]>; Dane Long <
> [email protected]>; Skyler Bilbo <[email protected]>
> Subject: Re: [EXTERNAL] Noncontinuous obstructions More than 18" down
>
> My understanding of the standard is no additional protection is needed as
> long as you have the 18" of clearance between the sprinkler and the top of
> the obstruction.  As you stated, the pattern is developed sufficiently to
> allow adequate protection since water will be delivered on both sides of
> the obstructions.
>
> *The above is my opinion and has not been processed as a formal
> interpretation in accordance with the NFPA Regulations Governing Committee
> Projects. This is provided with the understanding that the AFSA assumes no
> liability for this opinion or actions taken on it and they are not to be
> considered the official position of the AFSA, NFPA or NFPA's technical
> committees. AFSA cannot provide design or consulting engineering services,
> and this opinion should therefore not be considered, nor relied upon, as
> such.*
>
> Thanks,
> John
>
> John August Denhardt, PE
> *Vice President, Engineering and Technical Services*
>
> *American Fire Sprinkler Association*
> m: p: 301-343-1457
> 214-349-5965 ext 121
> w: firesprinkler.org
> <
> https://urldefense.proofpoint.com/v2/url?u=https-3A__www.facebook.com_firesprinkler.org_&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=dE_ALmGW3CHaFJIa1qPVLZpyrhiKK9Q6pwnWic9Kb74&s=BZdIbAOiOpzb7zeMSyXRk7uLyyR6OFVrhuVWUfDEvvM&e=
> > <
> https://urldefense.proofpoint.com/v2/url?u=https-3A__twitter.com_afsa_status_1039528345367732224&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=dE_ALmGW3CHaFJIa1qPVLZpyrhiKK9Q6pwnWic9Kb74&s=rgZGhkVIEiOkxv7HF0k1dibEsbMBuX-VGP-f93fSO8U&e=
> > <
> https://urldefense.proofpoint.com/v2/url?u=https-3A__www.linkedin.com_company_american-2Dfire-2Dsprinkler-2Dassociation-2Dafsa-2D_&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=dE_ALmGW3CHaFJIa1qPVLZpyrhiKK9Q6pwnWic9Kb74&s=q7u9PEOPcL28Jkuawdg_gajxoP_Wz9VXBIZ-7AoKK2I&e=
> >
>    <
> https://urldefense.proofpoint.com/v2/url?u=https-3A__www.instagram.com_firesprinklerorg_&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=dE_ALmGW3CHaFJIa1qPVLZpyrhiKK9Q6pwnWic9Kb74&s=RqqX_n3FmBVW0QSNLTzcmgf-0_7yqQkw_5hraWbfMYA&e=
> >
>
> *Our members are at the heart of everything we do*
>
>
> *Be a Member, Get a Member*
>
> We’re introducing many new programs to help meet your team’s business
> needs. AFSA is offering a six-month trial membership for contractors and a
> 12-month trial membership for municipal AHJs. Let’s help potential members
> see what they’re missing! Current members who recruit a new contractor
> member will receive a $100 gift card and the new member gets a free
> webinar.  Let’s grow stronger together! Join AFSA <
> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.firesprinkler.org_join&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=dE_ALmGW3CHaFJIa1qPVLZpyrhiKK9Q6pwnWic9Kb74&s=_3Ly_BO9z3thS1nj7D6ZziSXgla_RERUlFcjERAE84Y&e=
> >.
>
>
> On Mon, Feb 15, 2021 at 10:12 AM Dane Long via Sprinklerforum <
> [email protected]> wrote:
>
> > I don’t think these classify as a cloud ceiling as their 4ft by 8ft
> > tectum ceiling panels suspended below the desk. Per A8.6.5.3.3 Ceiling
> > panels with the width 4ft or less and the length 4ft or more and more
> > than 18" down do not require protection. NFPA 13 doesn’t specify a max
> > or min. spacing between ceiling panels. These panels are spaced
> > minimum 6" between and sloped in two directions (See Attached for some
> snips).
> >
> > Thanks,
> >
> > Dane Long, AET
> > Engineering Technician | Bamford Fire Sprinkler Co., Inc.
> > P:    785.825.7710
> > F:    785.825.0667
> > A:   1383 W. North Street Salina, KS  67401
> >
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum <[email protected]>
> > On Behalf of Skyler Bilbo via Sprinklerforum
> > Sent: Friday, February 12, 2021 5:36 PM
> > To: [email protected]
> > Cc: Skyler Bilbo <[email protected]>
> > Subject: Re: [EXTERNAL] Noncontinuous obstructions More than 18" down
> >
> > It sounds like the architect is working hard to inspire kids with his
> > beautiful ceiling design...  From the little information you gave, it
> > may be more like a cloud ceiling than a traditional obstruction.  See
> > section
> > 3.3.5.1 for the definition, and then 8.15.1.2.1.3 for criteria.  You
> > may also want to check out the research that "inspired" the cloud
> > ceiling criteria at the link below, it is really great information.
> >
> >
> > https://urldefense.proofpoint.com/v2/url?u=https-3A__www.nfpa.org_News
> > -2Dand-2DResearch_Fire-2Dstatistics-2Dand-2Dreports_Research-2Dreports
> > _Suppression_Sprinkler-2DProtection-2Dfor-2DCloud-2DCeilings&d=DwIGaQ&
> > c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A
> > &m=dE_ALmGW3CHaFJIa1qPVLZpyrhiKK9Q6pwnWic9Kb74&s=W8eQ1L2e0rGqQRs39FSMB
> > VSvuUNAZSPTj_xaVpb7Ktg&e=
> >
> >
> > Skyler Bilbo
> >
> > On Fri, Feb 12, 2021 at 3:41 PM Kyle.Montgomery via Sprinklerforum <
> > [email protected]> wrote:
> >
> > > Does "at least 1 inch of space between each panel" mean several feet
> > > of space between each panel, or does it mean just a couple of inches.
> > >
> > > To me, it sounds more like you would have to treat them as grouped
> > > obstructions and protect underneath.
> > >
> > > -Kyle M
> > >
> > > -----Original Message-----
> > > From: Sprinklerforum
> > > <[email protected]>
> > > On Behalf Of Dane Long via Sprinklerforum
> > > Sent: Friday, February 12, 2021 2:29 PM
> > > To: [email protected]
> > > Cc: Dane Long <[email protected]>
> > > Subject: [EXTERNAL] Noncontinuous obstructions More than 18" down
> > >
> > > Seeking others opinions....
> > >
> > > I'm doing an Elementary school where in the commons area they have
> > > 4ft. by 8ft. tectum ceiling panels space throughout with at least 1"
> > > of space between each panel. These panels are slopes with the roof
> > > in one direct and then away from the roof in another. A8.6.5.3.3 Per
> > > NFPA
> > > 13 (2016)
> > >
> > > "A.8.6.5.3.3 When obstructions are located more than 18 in. (450 mm)
> > > below the sprinkler deflector, an adequate spray pattern develops
> > > and obstructions up to and including 4 ft (1.2 m) wide do not
> > > require additional protection underneath. Examples are ducts, decks,
> > > open grate flooring, catwalks, cutting tables, overhead doors,
> > > soffits, ceiling panels, and other similar obstructions. The width
> > > of an object is the lesser of the two horizontal dimensions (with
> > > the length being the longer horizontal dimension). Sprinkler
> > > protection is not required under objects where the length is greater
> > > than 4 ft (1.2 m) and the width is 4 ft (1.2 m) or less."
> > >
> > > Doesn’t seem to me like I need protection below these panels.
> > >
> > > *Send me a private email if you'd like to look at the pdf.
> > >
> > > Thanks,
> > >
> > > Dane Long, AET
> > > Engineering Technician | Bamford Fire Sprinkler Co., Inc.
> > > P:    785.825.7710
> > > F:    785.825.0667
> > > A:   1383 W. North Street  Salina, KS  67401
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: Sprinklerforum
> > > <[email protected]>
> > > On Behalf Of Ron Greenman via Sprinklerforum
> > > Sent: Friday, February 12, 2021 2:35 PM
> > > To: [email protected]
> > > Cc: Ron Greenman <[email protected]>
> > > Subject: Re: Multiple System Calculation
> > >
> > > This sounds like a job for more sheetrock. Oh, and more cowbell is
> > > always good.
> > >
> > > On Fri, Feb 12, 2021 at 10:57 AM Sean Conlin via Sprinklerforum <
> > > [email protected]> wrote:
> > >
> > > > See NFPA-13, 23.4.4.1.1.4 and 23.4.4.1.1.5.
> > > >
> > > >
> > > >
> > > > This should help you with the engineer.
> > > >
> > > >
> > > > Regards,
> > > >
> > > > Sean W. Conlin, A.Sc.T.
> > > > Director
> > > > Demand Sprinkler Design Inc.
> > > > 37 Summerfield Crescent
> > > > Brampton, ON L6X 4K4
> > > > T: 905-216-0922
> > > > C: 416-317-0028
> > > > E: [email protected]
> > > >
> > > > This message, including any attachments is considered confidential
> > > > and for use only by the intended recipient(s).
> > > > Any other distribution, copying or disclosure is strictly prohibited.
> > > > Please delete this communication and notify Demand Sprinkler
> > > > Design Inc. if you are not the intended recipient or have received
> > > > this message in error. Demand Sprinkler Design Inc. accepts no
> > > > responsibility or liability for any loss or damage from use,
> > > > including damage from viruses.
> > > >
> > > >
> > > >
> > > > -----Original Message-----
> > > > From: Joe Burtell <[email protected]>
> > > > Sent: February 11, 2021 1:47 PM
> > > > To: [email protected]
> > > > Subject: Multiple System Calculation
> > > >
> > > >
> > > >
> > > > I have a situation where an engineer is telling me I have to
> > > > calculate a wet and dry system together because neither space
> > > > meets the 1500 s.f minimum. I have a penthouse mechanical room OH
> > > > 1 (WET) of
> > 1014 s.f.
> > > > and an adjacent room OH1 (DRY) of 469 s.f. I have calculated each
> > > > room separate of each other. There is a full-height wall with a
> > > > door that separates the rooms. The wall and door are not fire
> > > > rated, so the large room method is out. This does not make any sense
> to me.
> > > > Any sections that would require this to be done. He is saying
> > > > 11.1.2 of NFPA 13 2016 requires it. I argue exception #2 says it
> > > > does not
> > apply.
> > > >
> > > >
> > > >
> > > > Best regards,
> > > >
> > > >
> > > >
> > > > *Joe Burtell, SET, CFPS*
> > > >
> > > >
> > > >
> > > > [image: Burtell Fire_Small]
> > > >
> > > >
> > > >
> > > > Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
> > > >
> > > >
> > > >
> > > > 116 N. 11th Street | Billings, MT 59101
> > > >
> > > >
> > > >
> > > > Email: [email protected]<mailto:[email protected]>
> > > >
> > > >
> > > >
> > > > Web Site:
> > > > https://urldefense.proofpoint.com/v2/url?u=http-3A__www.burtellfire.
> > > > co
> > > > m&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8et
> > > > xB
> > > > 7n
> > > > LN8OBJwQd9A&m=YiHEM_F8z0hFdXcjHH1CqWJ0eIkSBYspd-WeDgZrxAI&s=Ur5xEx
> > > > eU
> > > > b- o3ipcDAOmkBHLKgAtIDEQsMndg_0EjUcg&e=
> > > >
> > > >
> > > >
> > > > *“**The bitterness of poor quality remains long after the
> > > > sweetness of low price is forgotten.**”*
> > > >
> > > >
> > > >
> > > > *NOTICE:*  The information contained in this e-mail transmission
> > > > is intended only for use of the individual or entity named above.
> > > > This e-mail transmission, and any documents, files, previous
> > > > e-mail transmissions or other information attached to it, may
> > > > contain confidential information that is legally privileged.  If
> > > > you are not the intended recipient of this e-mail transmission, or
> > > > the employee or agent responsible for delivering it to the
> > > > intended recipient, you are hereby notified that any disclosure,
> > > > dissemination, distribution, copying or other use of this
> > > > transmission or any of the information contained in or attached to
> > > > this e-mail is strictly prohibited.  If you have received this
> > > > e-mail transmission in error, please immediately notify us by
> > > > return e-mail transmission and destroy the original e-mail
> > > > transmission as well as its attachments without reading
> > > or saving it in any manner.  Thank you.
> > > >
> > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > >
> > > > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firespri
> > > > nk
> > > > le
> > > > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkl&d=DwIGaQ&c=wn3mZQL
> > > > Iu
> > > > In
> > > > h2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=YiHEM_
> > > > F8
> > > > z0
> > > > hFdXcjHH1CqWJ0eIkSBYspd-WeDgZrxAI&s=nlsG4VxOfTf_UUzkx-rk2ydjg94Xok
> > > > Zb
> > > > 0n
> > > > Q1PfqK6y0&e=
> > > > er.org
> > > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprink
> > > le
> > > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3
> > > mZ
> > > QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Yi
> > > HE
> > > M_F8z0hFdXcjHH1CqWJ0eIkSBYspd-WeDgZrxAI&s=LM0CNMnj-rd36HlSudxjbeoR5n
> > > CG
> > > KZrNT_CE45iTC5U&e=
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprink
> > > le
> > > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3
> > > mZ
> > > QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Yi
> > > HE
> > > M_F8z0hFdXcjHH1CqWJ0eIkSBYspd-WeDgZrxAI&s=LM0CNMnj-rd36HlSudxjbeoR5n
> > > CG KZrNT_CE45iTC5U&e=
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprink
> > > ler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkl&d=DwIGaQ&c=wn3mZQL
> > > IuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=dE_A
> > > LmGW3CHaFJIa1qPVLZpyrhiKK9Q6pwnWic9Kb74&s=Gr7-w7ZcTNOVrd7B3luoa5-AqW
> > > ZEhLJkrT59Qbt3W1A&e=
> > > er.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle
> > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZ
> > QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=dE_A
> > LmGW3CHaFJIa1qPVLZpyrhiKK9Q6pwnWic9Kb74&s=FpIS81LlHplCDk2Tv7eRH0MK4d0Z
> > s6ryz_U1qXknjIc&e= _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle
> > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZ
> > QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=dE_A
> > LmGW3CHaFJIa1qPVLZpyrhiKK9Q6pwnWic9Kb74&s=FpIS81LlHplCDk2Tv7eRH0MK4d0Z
> > s6ryz_U1qXknjIc&e=
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=dE_ALmGW3CHaFJIa1qPVLZpyrhiKK9Q6pwnWic9Kb74&s=FpIS81LlHplCDk2Tv7eRH0MK4d0Zs6ryz_U1qXknjIc&e=
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to