If it were me, my thought would be to just informally come up with a demand 
GPM.  Since presumably you know what is protected, and what sort of sprinklers 
are protecting it, you should be able to reasonably derive at least what 
current protection would require in CMDA/CMSA or ESFR format.  From there it's 
not difficult to come up with area x density or sqrt p x k x number of heads to 
get a GPM, add 10-20% for safety, you have a pretty good number.  Arguably 
anyone willing to do a BFP forward flow test ought to be willing to cover the 
expense of a system analysis, but if they're just required to make a forward 
flow test per a local ordinance obviously that's a different animal.  This is 
one where I'd propose my outline to the powers that be and try and get a buy 
off and make sure I present it with a fair dose of "this isn't ideal but it's 
reasonable for all involved" language.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Taylor and Sons via Sprinklerforum
Sent: Sunday, April 11, 2021 7:35 PM
To: [email protected]
Cc: Taylor and Sons <[email protected]>
Subject: Back flow flow test

 
BE ADVISED - This email originated outside EMCOR. 
 

NFPA 25 2014 Edition, section 
https://urldefense.com/v3/__http://13.6.2.1__;!!FaxH778!MWxxSdwC4aul1GvyK2yjr16b8YTkH2imuAChbtrocRXhVEXmsYwa-ecyIP2PsI46$
 

I have a 6” Ames 2000 SS that I need to forward flow test. Down stream of the 
#2 OS&Y control valve I have a 6” elbow, a 12” section of 6” pipe on the 
vertical, Then a 6x6x4 tee (4” to the FDC), then on top if the Tee a 6 “ dry 
valve.  
https://urldefense.com/v3/__http://13.6.2.1__;!!FaxH778!MWxxSdwC4aul1GvyK2yjr16b8YTkH2imuAChbtrocRXhVEXmsYwa-ecyIP2PsI46$
  says we shall exercise annually at minimum flow rate of the system demand.  
But guess what. There is not a Hydraulic nameplate. It would be easy to flip 
the FDC check valve and flow out thru the FDC siamese connection, but not if it 
will not meet the system demand. My question is, without the owner providing 
what that demand is, how do I know if the 4” FDC method will be enough? Or do I 
remove the 6” elbow and install a tee and some fittings and pipe to flow the 
full 6” out the door which is about 6’ away.

Thanks



John Taylor
[email protected]

Wrangell, AK 99929

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!MWxxSdwC4aul1GvyK2yjr16b8YTkH2imuAChbtrocRXhVEXmsYwa-ecyIH0pEydS$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • Back flow flow test Taylor and Sons via Sprinklerforum
    • RE: Back flow flow test Mike Morey via Sprinklerforum

Reply via email to