If it were me, my thought would be to just informally come up with a demand GPM. Since presumably you know what is protected, and what sort of sprinklers are protecting it, you should be able to reasonably derive at least what current protection would require in CMDA/CMSA or ESFR format. From there it's not difficult to come up with area x density or sqrt p x k x number of heads to get a GPM, add 10-20% for safety, you have a pretty good number. Arguably anyone willing to do a BFP forward flow test ought to be willing to cover the expense of a system analysis, but if they're just required to make a forward flow test per a local ordinance obviously that's a different animal. This is one where I'd propose my outline to the powers that be and try and get a buy off and make sure I present it with a fair dose of "this isn't ideal but it's reasonable for all involved" language.
Mike Morey CFPS 3229 • NICET S.E.T. 123677 Project Manager • Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive • Fort Wayne, IN • 46825 direct 260.487.7824 / cell 260.417.0625 / fax 260.487.7991 email [email protected] -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Taylor and Sons via Sprinklerforum Sent: Sunday, April 11, 2021 7:35 PM To: [email protected] Cc: Taylor and Sons <[email protected]> Subject: Back flow flow test BE ADVISED - This email originated outside EMCOR. NFPA 25 2014 Edition, section https://urldefense.com/v3/__http://13.6.2.1__;!!FaxH778!MWxxSdwC4aul1GvyK2yjr16b8YTkH2imuAChbtrocRXhVEXmsYwa-ecyIP2PsI46$ I have a 6” Ames 2000 SS that I need to forward flow test. Down stream of the #2 OS&Y control valve I have a 6” elbow, a 12” section of 6” pipe on the vertical, Then a 6x6x4 tee (4” to the FDC), then on top if the Tee a 6 “ dry valve. https://urldefense.com/v3/__http://13.6.2.1__;!!FaxH778!MWxxSdwC4aul1GvyK2yjr16b8YTkH2imuAChbtrocRXhVEXmsYwa-ecyIP2PsI46$ says we shall exercise annually at minimum flow rate of the system demand. But guess what. There is not a Hydraulic nameplate. It would be easy to flip the FDC check valve and flow out thru the FDC siamese connection, but not if it will not meet the system demand. My question is, without the owner providing what that demand is, how do I know if the 4” FDC method will be enough? Or do I remove the 6” elbow and install a tee and some fittings and pipe to flow the full 6” out the door which is about 6’ away. Thanks John Taylor [email protected] Wrangell, AK 99929 _______________________________________________ Sprinklerforum mailing list [email protected] https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!MWxxSdwC4aul1GvyK2yjr16b8YTkH2imuAChbtrocRXhVEXmsYwa-ecyIH0pEydS$ This message is for the named person's use only. It may contain confidential, proprietary or legally privileged information. No confidentiality or privilege is waived or lost by any mistransmission. If you receive this message in error, please immediately delete it and all copies of it from your system, destroy any hard copies of it and notify the sender. You must not, directly or indirectly, use, disclose, distribute, print, or copy any part of this message if you are not the intended recipient. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org