Smarter guys on the forum than me I'm sure will correct me if I am wrong, but I 
don't think there is a prohibition about mixing orifice sizes.  Only mixing 
thermal sensitivity (QR and SR).  NFPA 13 8.3.3.2

Micah Davis
Principal
Phone1: (904) 800-6782
 Phone2: (931) 242-1299


4373 Sycamore Pass Ct W
Jacksonville, FL 32258



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Monday, April 19, 2021 2:24 PM
To: [email protected]
Cc: [email protected]
Subject: Same size orifice in a room

I'm trying to locate the section in the standard about all sprinklers in a 
compartment to be same orifice.  Can anyone help point me in that direction?  
My searching is not too productive today.

Travis Mack, CFPS, CWBSP, RME-G, COC, SET Engineering Manager MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271 ext. 700 C: 480-272-2471
[email protected]<mailto:[email protected]>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to