23.4.4.9 (2016  ed NFPA 13) is the only prohibitions about mixing sprinkler 
sizes I'm aware of.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Monday, April 19, 2021 2:24 PM
To: [email protected]
Cc: [email protected]
Subject: Same size orifice in a room

 
BE ADVISED - This email originated outside EMCOR. 
 

I'm trying to locate the section in the standard about all sprinklers in a 
compartment to be same orifice.  Can anyone help point me in that direction?  
My searching is not too productive today.

Travis Mack, CFPS, CWBSP, RME-G, COC, SET Engineering Manager MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271 ext. 700 C: 480-272-2471
[email protected]<mailto:[email protected]>
https://urldefense.com/v3/__http://www.mfpdesign.com__;!!FaxH778!Lo1PdKEjN9j3g4F1cPeRvfBxEdPjxO2gO0Fyus5x_1tEqJ6kbcuqG0oNByEJ4DUU$
 
<https://urldefense.com/v3/__http://www.mfpdesign.com__;!!FaxH778!Lo1PdKEjN9j3g4F1cPeRvfBxEdPjxO2gO0Fyus5x_1tEqJ6kbcuqG0oNByEJ4DUU$
 >

Send large files to us via: 
https://urldefense.com/v3/__https://www.hightail.com/u/MFPDesign__;!!FaxH778!Lo1PdKEjN9j3g4F1cPeRvfBxEdPjxO2gO0Fyus5x_1tEqJ6kbcuqG0oNByPCuocv$
 
<https://urldefense.com/v3/__https://na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D&reserved=0__;JSUlJSUlJSUlJSUlJSU!!FaxH778!Lo1PdKEjN9j3g4F1cPeRvfBxEdPjxO2gO0Fyus5x_1tEqJ6kbcuqG0oNBz5L-XIt$
 >

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!Lo1PdKEjN9j3g4F1cPeRvfBxEdPjxO2gO0Fyus5x_1tEqJ6kbcuqG0oNB9_2Ql-1$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to