If you do not need the pump to meet the fire flow requirements of the fire 
code, than you can size it for the sprinkler demand only.

In evaluating any water supply, you do not have to add the outside fire flow to 
the building system demand in any case. In your scenario, it would not be a 
2900 gpm demand it would be a system capable of delivering 2000 GPM at 20 PSI, 
or 900 GPM at whatever residual is required for the building system.


Steve Leyton

(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)



-------- Original message --------
From: Gregg Fontes via Sprinklerforum <[email protected]>
Date: 4/21/21 6:57 AM (GMT-08:00)
To: [email protected]
Cc: Gregg Fontes <[email protected]>
Subject: Fire Pump Sprk & Fire Flow Demand

If a fire pump supplies both the fire sprinkler system and the site fire 
hydrants, does the fire pump gpm need to be capable of suppling both?  (Fire 
sprinkler demand 900 gpm and site fire hydrant demand 2000 gpm for a total of 
2,900.  Can the fire pump be size at 750 for the fire sprinkler/hose demand or 
does it have to be a 2000 gpm so it can supply both the sprinkler and site fire 
hydrant flows of 2900 gpm?)  The supply is city water and there is a bypass on 
the fire pump.  The city supply comes into the fire pump house and goes out to 
single loop that supplies both the fire sprinkler systems and the site fire 
hydrants.  (The city flow and psi is adequate to meet the site fire flow at 
20-psi.)

Thanks,
Gregg Fontes

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to