Micah,

As per NFPA 13 (2013 edition) 17.1.2 Special Protection Criteria refers you to 
Figure 17.1.2.1. 
(See Section C.21). Figure 17.1.2.lstates that Group A -Exposed -Expanded is 
outside the scope of 
Chapter 17.  

Per NFPA  13 - 2013 Edition Appendix comment -"A.17.1.2.1 All arrangements of 
exposed plastics cannot 
be protected with all types of sprinklers. Only certain combinations of ceiling 
sprinklers and in 
rack sprinklers have been found to provide acceptable protection. No full-scale 
fire testing has 
been performed that has determined acceptable criteria for exposed expanded 
plastics. Factory 
Mutual has published  criteria in its data sheets to protect exposed expanded 
plastics based on a 
risk analysis and small/intermediate-scale  test data. Some authorities having 
jurisdiction  accept 
that criteria as an alternative to the intent of NFPA 13."  

The specific section of FM Data Sheet 8-9 is Design Scheme 8-9A is on page 47 
of FM data sheet 8-9 interim revision January 2020. 
This design scheme permits the protection of exposed expanded foam stored in 
racks - with in-rack sprinklers and horizontal barriers without having to 
increase ceiling level sprinkler densities or having to balance with ceiling 
system, in addition you only have to supply water to the most demanding of 
either the ceiling system 
or in-rack sprinklers only, not both. 

Hope this helps.

Jim Davidson 

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Micah Davis via Sprinklerforum
Sent: Thursday, April 29, 2021 10:39 AM
To: SprinklerForum <[email protected]>
Cc: Micah Davis <[email protected]>
Subject: Exposed unexpanded Group A plastic storage

I have a warehouse that will store some exposed unexpanded Group A plastic 
(sheet plastic in rolls).  The rest of the storage will be Class III 
commodities.  All stored on racks.  Building height is 35 ft and with racks up 
to 25 ft.  NFPA 13 - 17.2.1.3 states, "For storage of Group A plastics between 
5 ft and 12 ft in height, the installation requirements for extra hazard 
systems shall apply."  We have the ability in this case to stipulate that the 
plastic storage be limited to 12 ft or less in height (I understand all of the 
human behavior questions that arise about warehouse workers actually abiding by 
this).  My question is, does 17.2.1.3 give instruction only for installation 
guidance (sprinkler spacing, obstructions, etc.) or does this allow me to use 
AT LEAST extra hazard design criteria for protection of the low-piled plastic?  
Specifically, if the plastic is limited to 12 ft, could the rest of the 
warehouse be protected with a protection scheme adequate for the Class III comm
   odities and if that scheme exceeds the demands of extra hazard densities, 
the plastic is considered protected?

My gut is that the section refers only to installation procedures and I am 
stuck with the requirements of 17.2.1.4, 17.2.2, or 17.2.3 for design criteria 
even is the plastic storage is limited to 12 ft.

Thank you,
Micah Davis
Dynamic Fire Designs, LLC

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to