I have a warehouse that will store some exposed unexpanded Group A plastic 
(sheet plastic in rolls).  The rest of the storage will be Class III 
commodities.  All stored on racks.  Building height is 35 ft and with racks up 
to 25 ft.  NFPA 13 - 17.2.1.3 states, "For storage of Group A plastics between 
5 ft and 12 ft in height, the installation requirements for extra hazard 
systems shall apply."  We have the ability in this case to stipulate that the 
plastic storage be limited to 12 ft or less in height (I understand all of the 
human behavior questions that arise about warehouse workers actually abiding by 
this).  My question is, does 17.2.1.3 give instruction only for installation 
guidance (sprinkler spacing, obstructions, etc.) or does this allow me to use 
AT LEAST extra hazard design criteria for protection of the low-piled plastic?  
Specifically, if the plastic is limited to 12 ft, could the rest of the 
warehouse be protected with a protection scheme adequate for the Class III comm
 odities and if that scheme exceeds the demands of extra hazard densities, the 
plastic is considered protected?

My gut is that the section refers only to installation procedures and I am 
stuck with the requirements of 17.2.1.4, 17.2.2, or 17.2.3 for design criteria 
even is the plastic storage is limited to 12 ft.

Thank you,
Micah Davis
Dynamic Fire Designs, LLC