Owen:

What exactly do you object to if the fire official is trying to verify the 
delivery of adequate fire flow?   What water company or muni-utilities 
department is providing the water?   Have they exercised any hydrants in the 
subject neighborhood in the past... I dunno, TEN years?    Can you, sitting at 
your keyboard, verify that the required fire flow is available and there are no 
closed sectional valves in the neighborhood?    That the ancient 6" that was 
installed right after WW2 isn't bleeding residual pressure during a fire flow 
event?    We have at least 6 water companies just in San Diego County that have 
utterly failed to maintain and improve their systems as development adds 
density to their service areas so now they use velocity limits as a 
hair-trigger benchmark and they require developers to put in sometimes hundreds 
of feet of new 8" to replace their aging infrastructure so they don't have to 
put it in next year's budget.    What do you think is worse, a $500 flow model 
or a $500,000 section of new main?

Instead of just sniping at a non-problem, trying called the FPO who's made this 
ruling and ask them if they're aware of issues with that water company or 
perhaps that zone of the water company's system.    Advise your clients on 
future projects that this charge might be imposed.   Proactively call the water 
company to find out if they have archival flow tests or models that might 
satisfy the fire official.    Yes, it's $500 and will apparently take two weeks 
(that's a separate issue and BS IMHO).   
And yes perhaps it's unusual to see this request on an SFR, but we have to 
prove fire flow on every project, so maybe-just-maybe this fire official knows 
something about the water system in question. 


Steve Leyton, President
Protection Design and Consulting
T  |  619.255.8964 x 102  |  www.protectiondesign.com 
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Owen Evans via Sprinklerforum
Sent: Monday, June 14, 2021 6:54 AM
To: Travis Mack via Sprinklerforum <[email protected]>
Cc: Owen Evans <[email protected]>
Subject: Fire Flow Test for SFR

Has anyone had an AHJ require a fire flow test for a single family residence 
situated in a metropolitan area? Not for the purpose of calculations but to 
ensure the municipal water delivery system could handle  the 500 gpm required 
(1000 gpm per California Residential Fire Code minus a 500 gpm credit for 
having fire sprinklers). This is a waste of time and money. It takes 
approximately four weeks to get done by water company, at a cost of $500. Has 
anyone argued against such a requirement, and how? I tried but was met with 
“because I wear a badge and I say so”. The general didn’t want to argue with 
AHJ, he decided to pay to avoid any further delay. 

Owen Evans



Sent from the all new Aol app for iOS
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to