Even though the standard does not require it, as another old fire guy, I prefer 
that the sprinkler be located towards the closet door and not above the top 
shelf.  Seen blankets on the top shelf bury the sprinkler such that a fire in 
the closet never activated the sprinkler due to the warm, soft insulation of 
the blankets.  Nobody got hurt, but the fire grew bigger than it needed to.
Regards,Dwight HavensAnother old fire guy.