NFPA 13 (2019 edition) states the following in two sections:

9.5.5.4 Closets. In all closets and compartments, including
those closets housing mechanical equipment, that are not
larger than 400 ft3 (11 m3) in size, a single sprinkler at the
highest ceiling level shall be sufficient without regard to
obstructions or minimum distance to the wall.
9.5.6 Clearance from Deflector to Storage.
9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
9.5.6.5 are met, the clearance between the deflector and the
top of storage or contents of the room shall be 18 in. (450 mm)
or greater.

Section 9.5.5.4 states "....a single sprinkler at the highest ceiling level 
shall be sufficient without regard to obstructions or minimum distance to the 
wall."  Does 9.5.5.4 allow a sprinkler to be less than 18 inches from the 
storage in a closet?  Section 9.5.6.1 does not specifically say that 9.5.5.4 is 
an exception to the 18 inch storage clearance requirement.

However, if the storage less than 18 inches from the deflector is considered an 
"obstruction", then it would seem that 9.5.5.4 would allow storage that is less 
than 18 inches from the sprinkler deflector in a closet.

Thanks in advance.

Pete
Dept of VA