2019 9.2.2 Spaces Under Ground Floors, Exterior Docks, and Platforms or possibly this one. 9.2.10* Equipment Enclosures. Sprinklers shall not be required to be installed within electrical equipment, mechanical equipment, or air handling units not intended for occupancy. It is not the intent of 9.2.10 to require sprinklers to be installed in air handling units (AHUs) or in similar mechanical or electrical equipment. AHUs for large buildings and building complexes can be so large that it brings into question whether sprinklers should be installed inside them. Providing sprinkler protection in such units is not practical and would not be overly effective based on the limited hazard present. A.9.2.10 Equipment having access for routine maintenance should not be considered as intended for occupancy. AHUs that have access panels or “man doors" are not necessarily intended for occupancy and should not be treated as such when applying 9.2.10. Often the presence of an access hatch or other means to allow for equipment maintenance is misconstrued as allowing occupancy of such a space.
Best regards, *Joe Burtell, SET, CFPS* [image: Burtell Fire_Small] Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>* 116 N. 11th Street | Billings, MT 59101 Email: [email protected] Web Site: http://www.burtellfire.com *“**The bitterness of poor quality remains long after the sweetness of low price is forgotten.**”* *NOTICE:* The information contained in this e-mail transmission is intended only for use of the individual or entity named above. This e-mail transmission, and any documents, files, previous e-mail transmissions or other information attached to it, may contain confidential information that is legally privileged. If you are not the intended recipient of this e-mail transmission, or the employee or agent responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, dissemination, distribution, copying or other use of this transmission or any of the information contained in or attached to this e-mail is strictly prohibited. If you have received this e-mail transmission in error, please immediately notify us by return e-mail transmission and destroy the original e-mail transmission as well as its attachments without reading or saving it in any manner. Thank you. On Thu, Aug 5, 2021 at 5:11 AM Tyson Sutherland via Sprinklerforum < [email protected]> wrote: > Todd, > > I work on a job that had this same scenario. We had to put sprinklers down > there because it was accessible for maintenance. It was like a concrete > vault, and we had to core drill a hole for a feed. > > > TYSON SUTHERLAND, CET > NICET Level III Design Technician > Ohio ASSD #8495 > > 2900 Newpark Drive > Barberton, OH 44203 > > 888-857-2817 x317 > 330-600-0697 Cell > [email protected] > > -----Original Message----- > From: Sprinklerforum <[email protected]> On > Behalf Of Fpdcdesign via Sprinklerforum > Sent: Wednesday, August 4, 2021 7:56 PM > To: Sprinklerforum <[email protected]> > Cc: Fpdcdesign <[email protected]> > Subject: Pool maintenance area > > > BE ADVISED - This email originated outside EMCOR. > > > > > > I am working on a project with a therapy pool that is recessed into the > floor with its own pit. There is a service area (stand up height) in the > pit adjacent to the pool for maintenance. The walls, ceiling and floor are > concrete and the pool enclosure is metal. Sprinklers in the service area or > no? There is no good way to feed them > > > > Todd G Williams, PE > Fire Protection Design/Consulting > > Stonington, CT > > 860-535-2080 (tel:860-535-2080) (ofc) > > 860-554-7054 (tel:860-554-7054) (fax) > > 860-608-4559 (tel:860-608-4559) (cell) > > > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!NIgYE1Vt-fpoUIOn-Fkc8jaJAKd4isi2kNKARrKFBGFYBaIP1X0S_02W-rH1UlP6UcWTtaM$ > > This message is for the named person's use only. It may contain > confidential, proprietary or legally privileged information. No > confidentiality or privilege is waived or lost by any mistransmission. If > you receive this message in error, please immediately delete it and all > copies of it from your system, destroy any hard copies of it and notify the > sender. You must not, directly or indirectly, use, disclose, distribute, > print, or copy any part of this message if you are not the intended > recipient. > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org