I think the standard makes a distinction between large equipment with internal 
access and mechanical/equipment rooms.  Being a mechanical/equipment room, your 
answer will boil down to the ease of access and the likelihood the owner (or 
their maintenance personnel)  will use the open space for storage.  

I'm working on a small hospital that has a hydro-therapy room - very similar to 
what you describe.  In this case, maintenance access is via a trap door in the 
pool deck and steep ladder leading down to the pit.  I wouldn't expect large 
quantities of storage, but the less-than-impossible access combined with the 
open space - we're sprinklering it.

Ed K



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Joe Burtell via Sprinklerforum
Sent: Thursday, August 5, 2021 7:48 AM
To: [email protected]
Cc: Joe Burtell <[email protected]>; Tyson Sutherland 
<[email protected]>
Subject: Re: Pool maintenance area

2019 9.2.2 Spaces Under Ground Floors, Exterior Docks, and Platforms or 
possibly this one.
9.2.10* Equipment Enclosures. Sprinklers shall not be required to be installed 
within electrical equipment, mechanical equipment, or air handling units not 
intended for occupancy.
It is not the intent of 9.2.10 to require sprinklers to be installed in air 
handling units (AHUs) or in similar mechanical or electrical equipment.
AHUs for large buildings and building complexes can be so large that it brings 
into question whether sprinklers should be installed inside them.
Providing sprinkler protection in such units is not practical and would not be 
overly effective based on the limited hazard present.
A.9.2.10 Equipment having access for routine maintenance should not be 
considered as intended for occupancy.
AHUs that have access panels or “man doors" are not necessarily intended for 
occupancy and should not be treated as such when applying 9.2.10. Often the 
presence of an access hatch or other means to allow for equipment maintenance 
is misconstrued as allowing occupancy of such a space.


Best regards,

*Joe Burtell, SET, CFPS*

[image: Burtell Fire_Small]

Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*

116 N. 11th Street | Billings, MT 59101

Email: [email protected]

Web Site: http://www.burtellfire.com

*“**The bitterness of poor quality remains long after the sweetness of low 
price is forgotten.**”*

*NOTICE:*  The information contained in this e-mail transmission is intended 
only for use of the individual or entity named above.  This e-mail 
transmission, and any documents, files, previous e-mail transmissions or other 
information attached to it, may contain confidential information that is 
legally privileged.  If you are not the intended recipient of this e-mail 
transmission, or the employee or agent responsible for delivering it to the 
intended recipient, you are hereby notified that any disclosure, dissemination, 
distribution, copying or other use of this transmission or any of the 
information contained in or attached to this e-mail is strictly prohibited.  If 
you have received this e-mail transmission in error, please immediately notify 
us by return e-mail transmission and destroy the original e-mail transmission 
as well as its attachments without reading or saving it in any manner.  Thank 
you.


On Thu, Aug 5, 2021 at 5:11 AM Tyson Sutherland via Sprinklerforum < 
[email protected]> wrote:

> Todd,
>
> I work on a job that had this same scenario. We had to put sprinklers 
> down there because it was accessible for maintenance. It was like a 
> concrete vault, and we had to core drill a hole for a feed.
>
>
> TYSON SUTHERLAND, CET
> NICET Level III Design Technician
> Ohio ASSD #8495
>
> 2900 Newpark Drive
> Barberton, OH 44203
>
> 888-857-2817 x317
> 330-600-0697 Cell
> [email protected]
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> 
> On Behalf Of Fpdcdesign via Sprinklerforum
> Sent: Wednesday, August 4, 2021 7:56 PM
> To: Sprinklerforum <[email protected]>
> Cc: Fpdcdesign <[email protected]>
> Subject: Pool maintenance area
>
>
> BE ADVISED - This email originated outside EMCOR.
>
>
>
>
>
>   I am working on a project with a therapy pool that is recessed into 
> the floor with its own pit. There is a service area (stand up height) 
> in the pit adjacent to the pool for maintenance. The walls, ceiling 
> and floor are concrete and the pool enclosure is metal. Sprinklers in 
> the service area or no? There is no good way to feed them
>
>
>
>  Todd G Williams, PE
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
> 860-554-7054 (tel:860-554-7054)     (fax)
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cg
> i/sprinklerforum-firesprinkler.org__;!!FaxH778!NIgYE1Vt-fpoUIOn-Fkc8ja
> JAKd4isi2kNKARrKFBGFYBaIP1X0S_02W-rH1UlP6UcWTtaM$
>
> This message is for the named person's use only.  It may contain 
> confidential, proprietary or legally privileged information. No 
> confidentiality or privilege is waived or lost by any mistransmission.  
> If you receive this message in error, please  immediately delete it 
> and all copies of it from your system, destroy any hard copies of it 
> and notify the sender.  You must not, directly or indirectly, use, 
> disclose, distribute, print, or copy any part of this message if you 
> are not the intended recipient.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to