I am working on the renovation of an upscale bridal store where there a
several partial height walls being installed. The spaces created by the walls
are semi-private consulting areas. The top of the walls is 1’-10” below the
ceiling. The existing concealed sprinklers are spaced at roughly 10 ft x 10 ft.
NFPA 13 (2016) section 8.6.5.2.2 only addresses Light Hazard occupancies. Since
the store is Ordinary Hazard 2, that section is not applicable. What is? I was
looking at A.8.6.5.3.3 but that may be stretching it. Thoughts?