The NFPA 13 technical committee has addressed partial height walls in
ordinary hazard occupancies in the NFPA 13, 2022 edition.  Section
10.2.7.3.2.3 and 10.2.7.3.2.4 address partial height walls 12 in. or less
in width.  If a sprinkler is installed within 6 in. of the centerline of
the partial height wall the sprinkler shall be installed 6 in. or greater
vertically.  If installed greater than 6 in. of the centerline it shall be
installed 18 in. or greater.  This can be accessed as an NFPA member on
NFPA.org/13next.  Figures are provided to describe the requirements.

This language has passed the second revision ballot and is expected to be
published in the 2022 edition of NFPA 13.

The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the NFPA or its technical committees.
AFSA cannot provide design or consulting engineering services, and this
opinion should therefore not be considered, nor relied upon, as such.



On Tue, Sep 14, 2021 at 3:44 PM Fpdcdesign via Sprinklerforum <
[email protected]> wrote:

>
>
>
>   I am working on the renovation of an upscale bridal store where there a
> several partial height walls being installed. The spaces created by the
> walls are semi-private consulting areas. The top of the walls is 1’-10”
> below the ceiling. The existing concealed sprinklers are spaced at roughly
> 10 ft x 10 ft.
>
>
>
> NFPA 13 (2016) section 8.6.5.2.2 only addresses Light Hazard occupancies.
> Since the store is Ordinary Hazard 2, that section is not applicable. What
> is? I was looking at A.8.6.5.3.3 but that may be stretching it. Thoughts?
>
>
>
>  Todd G Williams, PE
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
> 860-554-7054 (tel:860-554-7054)     (fax)
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>


-- 
*Best Regards,*

Josh McDonald, MSET, CFPS
Technical Programs Specialist

*American Fire Sprinkler Association*
p: 214-349-5965 ext. 138
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Apprentice Trainers Wanted* It’s time to put your knowledge and experience
to work training the next generation of Fire Sprinkler Fitters and
Technicians. In preparation to deliver related technical instruction (RTI)
for national apprenticeship training, AFSA currently seeks qualified
instructors.  Click here <http://www.firesprinkler.org/trainers> for more
information.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to