Forumities,

This has likely been previously addressed, but it's just not coming back to
me . . .

 

I've got an existing ordinary hazard area that is protected by existing EC
sprinklers.  The existing EC sprinklers have fast response (3mm) elements
and are listed as standard-response for the 20'x20' spacing they are
protecting.  If these sprinklers were protecting an area of 14' x 14', they
would be listed as quick-response.

 

I need to add a couple standard-coverage sprinklers due to wall changes.
Should the new standard-coverage sprinklers be quick-response, or
standard-response?

 

NFPA 13 (2019) section 9.4.3.5 gives me guidance if I were adding an
identical EC sprinkler, but that's not what's happening.

 

Thanks in advance,

Ed K

 

 

 