I think making the new SC sprinklers standard-response is the best solution in this particular situation.
I could see these EC sprinklers being used as both 20'x20' and 14'x14' in the same compartment in order to protect odd-ball areas. Then adding new SC sprinklers and deciding if they should be QR or SR gets more complicated. I was hoping 13 would provide guidance. Ed -----Original Message----- From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Taylor Schumacher via Sprinklerforum Sent: Tuesday, October 12, 2021 2:31 PM To: sprinklerforum@lists.firesprinkler.org Cc: Taylor Schumacher <tay...@sfsprinkler.com> Subject: RE: mixing EC sprinks with SC sprinks We follow how they are listed. If the 3mm bulbs are spaced at SR, we utilize SR 5mm bulbs for adjacent standard coverage sprinklers. Taylor Schumacher -----Original Message----- From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Mike Morey via Sprinklerforum Sent: Tuesday, October 12, 2021 2:23 PM To: sprinklerforum@lists.firesprinkler.org Cc: Mike Morey <mmo...@shambaugh.com> Subject: RE: mixing EC sprinks with SC sprinks I would say if they're all being used as an SR sprinkler based on listing, I would put in SR sprinklers. Is there an AHJ you can lean on? That's what I would approach them with as far as logic. Mike Morey CFPS 3229 * NICET S.E.T. 123677 Project Manager * Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 / cell 260.417.0625 / fax 260.487.7991 email mmo...@shambaugh.com -----Original Message----- From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Ed Kramer via Sprinklerforum Sent: Tuesday, October 12, 2021 3:16 PM To: sprinklerforum@lists.firesprinkler.org Cc: Ed Kramer <e...@bamfordfire.com> Subject: mixing EC sprinks with SC sprinks BE ADVISED - This email originated outside EMCOR. Forumities, This has likely been previously addressed, but it's just not coming back to me . . . I've got an existing ordinary hazard area that is protected by existing EC sprinklers. The existing EC sprinklers have fast response (3mm) elements and are listed as standard-response for the 20'x20' spacing they are protecting. If these sprinklers were protecting an area of 14' x 14', they would be listed as quick-response. I need to add a couple standard-coverage sprinklers due to wall changes. Should the new standard-coverage sprinklers be quick-response, or standard-response? NFPA 13 (2019) section https://urldefense.com/v3/__http://9.4.3.5__;!!FaxH778!NjvBLXYl2Y98ErgMyq9iF VRSvqAUyYKBmSwdF1FH-Y30MG_-ngt9IAYtt0y1QUQd$ gives me guidance if I were adding an identical EC sprinkler, but that's not what's happening. Thanks in advance, Ed K _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/spri nklerforum-firesprinkler.org__;!!FaxH778!NjvBLXYl2Y98ErgMyq9iFVRSvqAUyYKBmSw dF1FH-Y30MG_-ngt9IAYttwf-jBd3$ This message is for the named person's use only. It may contain confidential, proprietary or legally privileged information. No confidentiality or privilege is waived or lost by any mistransmission. If you receive this message in error, please immediately delete it and all copies of it from your system, destroy any hard copies of it and notify the sender. You must not, directly or indirectly, use, disclose, distribute, print, or copy any part of this message if you are not the intended recipient. _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org