The operating sprinkler will receive water from two directions. That meets
more of the definition of gridded than it does loop.


The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the NFPA or its technical committees.
AFSA cannot provide design or consulting engineering services, and this
opinion should therefore not be considered, nor relied upon, as such.


Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE

Coordinator, Engineering and Technical Services

American Fire Sprinkler Association

[email protected]

214-349-5971


On Tue, Oct 26, 2021 at 1:38 PM Richard Carr via Sprinklerforum <
[email protected]> wrote:

> I think you could call it a looped dry system if it will make you feel
> better.
>
> Richard M. Carr, SET
> Project Manager/Design
> Diboco Fire Sprinklers, Inc.
> 325 Jackson Loop Road
> Flat Rock, NC  28731
>
> [email protected]
> 828-696-3400
> 828-696-2288 Fax
> 828-708-9118 Mobile
>
>
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of Ed Kramer via Sprinklerforum
> Sent: Tuesday, October 26, 2021 1:31 PM
> To: [email protected]
> Cc: Ed Kramer <[email protected]>
> Subject: Gridded dry system
>
> Is this sprinkler system a gridded system?   I've avoided this type of
> design in the past for dry systems because it 'kinda' a grid, but not
> really.  Now I'm questioning my questioning.  What are your thoughts?
>
>
>
> Reference NFPA 13 (2019) sections 8.2.3.10 and 3.3.206.5.
>
>
>
> https://www.dropbox.com/s/u2hw3cbvlga4fcq/Dry%20Attic%20System.pdf?dl=0
>
>
>
>
>
> Ed Kramer
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to