If you were to put caps on the left and right lines going north and south, it 
resembles a compound gridded system and a sprinkler can receive water from both 
sides. 

The east and west lines are essentially the mains and so is the 4" in the 
middle.

Yes is has a looped piping  arrangement and is symmetrical but it is a gridded 
system by NFPA-13 definition.  If you were to not tie the lines together, it 
would be a loop.

Regards,

Sean W. Conlin
E:[email protected]

This message, including any attachments is considered confidential and for use 
only by the intended recipient(s).
Any other distribution, copying or disclosure is strictly prohibited. Please 
delete this communication and notify 
Demand Sprinkler Design Inc. if you are not the intended recipient or have 
received this message in error. Demand
Sprinkler Design Inc. accepts no responsibility or liability for any loss or 
damage from use, including damage from viruses.

-----Original Message-----
From: Ed Kramer <[email protected]> 
Sent: October 26, 2021 1:31 PM
To: [email protected]
Subject: Gridded dry system

Is this sprinkler system a gridded system?   I've avoided this type of
design in the past for dry systems because it 'kinda' a grid, but not really.  
Now I'm questioning my questioning.  What are your thoughts?

 

Reference NFPA 13 (2019) sections 8.2.3.10 and 3.3.206.5.

 

https://www.dropbox.com/s/u2hw3cbvlga4fcq/Dry%20Attic%20System.pdf?dl=0

 

 

Ed Kramer

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org