For the safety of the installers so they do not have to climb up in the top of 
an attic or have to make make-shift ladders, I typically try to put the main 
down the middle for the BB's at chest high and use sprigs. This also helps with 
getting over mechanical equipment/duct that may be in the attic space. Then I 
run a low main around the outside edges, looped, to catch the sprinklers around 
the eves and any pendent sprinklers for the area below. When I use Attic 
Sprinklers I try my best to use CPVC if it is wet and the water supply is good. 
(Wet systems in attics. Maybe a Florida thing.)

Thank You,



Mickey Ferguson
Design Technician/Project Manager
Wayne Automatic Fire Sprinklers, Inc. (r)
222 Capitol Court Ocoee, FL 
34761<https://www.google.com/maps/place/Wayne+Automatic+Fire+Sprinklers/@28.5609916,-81.5534771,19.65z/data=!4m13!1m7!3m6!1s0x88e782fb5aadbabf:0xd7238f1eab6eb876!2s222+Capitol+Ct,+Ocoee,+FL+34761!3b1!8m2!3d28.5607736!4d-81.5533424!3m4!1s0x88e782fb33d24d9d:0x9e453facd228f6f7!8m2!3d28.5609763!4d-81.5532511>
ph: 4078775582<tel:4078775582> cell: 4079512009<tel:4079512009>
Ocoee<https://www.waynefire.com/locations/ocoee-florida-orlando> | 
Jacksonville<https://www.waynefire.com/locations/jacksonville-florida> | 
Deerfield Beach<https://www.waynefire.com/locations/deerfield-florida> | 
Tampa<https://www.waynefire.com/locations/tampa-florida> | Ft 
Myers<https://www.waynefire.com/locations/ft-meyers-florida> | Concord, 
NC<https://www.waynefire.com/locations/concord-north-carolina-charlotte>




From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Brian Harris via Sprinklerforum
Sent: Wednesday, October 27, 2021 7:04 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Brian Harris <[email protected]<mailto:[email protected]>>
Subject: Attic Piping

Seems were seeing more and more wood framed buildings these days and with that 
comes attics. Just curious what the general school of thought is with running 
piping in these spaces. Is it better to run the Main high under the ridges with 
back to back heads (size permitting) or is it better run Mains low and then run 
smaller Mains up the slope feeding branches at the ridges? I'm working on a job 
now that kinda resembles a long rectangle with no center (courtyards). I have 
all the heads laid out with B/B at the ridges, some AP's in the corners & 
throughout as needed. Just looking for ideas from some of you with much more 
attic experience than I have.

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com><http://bvssystemsinc.com/<http://bvssystemsinc.com>>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to