Tim,

If you have the handbook the next page actually talks about this with a
"Closer Look" at the height limitations. (2016 - Pg201)

Thanks,






Dane Long, AET
Engineering Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  67401



-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of tstone52--- via Sprinklerforum
Sent: Tuesday, November 9, 2021 2:42 PM
To: [email protected]
Cc: [email protected]
Subject: 13R Installation of Sprinkler Systems in Low-Rise Residential
Occupancies

Am I reading the Scope of 13R correctly?

 

I am designing a Sprinkler system for a building which is five stories in
height. Each floor is about 5,500 SF. The Ground floor is a parking garage
of concrete & steel (Type 1a construction) with 4 stories of Residential
above which constructed of wood (Type 3B Construction). The parking garage
shall be protected by a Dry Pipe System designed in accordance with NFPA 13.
There is a 2 hour Occupancy Separation between Garage & The Second Floor.
The Second thru Fifth levels are to be protected by a NFPA 13R Sprinkler
System. The overall building height measures less than 60' above grade.

 

NFPA 13R Scope:  states this standard shall cover ____ "residential
occupancies up to and including four stories in height in buildings not
exceeding 60 ft. in height above grade plane."

 

Due to the phrase "in Buildings" am I interpreting this correctly?

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

   117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968

              <mailto:[email protected]> [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to