Hope all is well with everyone.

Building codes are typically very clear on what characterizes a building to
be separate and distinct. Either build a building by itself, build multiple
buildings and separate by fire separation distance is specified by the
code, build two buildings right smack up against each other and separate by
an approved or listed firewall assembly, or use the special provision in
the IBC that applies typically to what we call podium-style buildings.

Section 510.2 of the 2018 IBC requires a horizontal assembly having a fire
resistance rating of not less than three hours for a single building to be
considered as separate and distinct buildings. A 2-hour fire separation
assembly effectively serves to separate fire areas, but, in my opinion, it
would not qualify a single structure to be considered as separate and
distinct buildings recognized by the building code.  Rather, it would be
categorized as a mixed occupancy, requiring NFPA 13 sprinkler protection
throughout.

Am I missing something?


On Tue, Nov 9, 2021 at 3:55 PM tstone52--- via Sprinklerforum <
[email protected]> wrote:

> Steve,
> That is exactly what the Architect that I am working for told me. The two
> hour Horizontal separation between the floors make this 2 separate
> buildings.
>
> Thank you.
>
> Regards,
> G. Tim Stone
>
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
>
>    117 Old Stage Rd. - Essex Jct., VT. 05452
> <https://www.google.com/maps/search/117+Old+Stage+Rd.+-+Essex+Jct.,+VT.+05452?entry=gmail&source=g>
> CELL: (802) 373-0638   TEL: (802) 434-2968
>              [email protected]
>
> -----Original Message-----
> From: Steve Leyton <[email protected]>
> Sent: Tuesday, November 9, 2021 3:51 PM
> To: [email protected]
> Cc: [email protected]
> Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise Residential
> Occupancies
>
> Assuming the building code that's applicable to this project classifies
> this
> as two separate buildings (a four-story Type 3 on a single-story Type 1
> podium), NFPA 13R can be used as a basis of design in many (most?)
> jurisdictions.   It is up to the building official to clarify whether a
> two-
> or three-hour separation is required between the podium and upper floors,
> but this is commonly viewed as two separate buildings.
>
> I have served as member of the NFPA Technical Committee for Residential
> Sprinklers, but this is MY opinion only.
>
>
> Steve Leyton, President
> Protection Design and Consulting
> T  |  619.255.8964 x 102  |  www.protectiondesign.com
> 2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108 Fire
> Protection System Design | Consulting | Planning | Training
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of tstone52--- via Sprinklerforum
> Sent: Tuesday, November 09, 2021 12:42 PM
> To: [email protected]
> Cc: [email protected]
> Subject: 13R Installation of Sprinkler Systems in Low-Rise Residential
> Occupancies
>
> Am I reading the Scope of 13R correctly?
>
>
>
> I am designing a Sprinkler system for a building which is five stories in
> height. Each floor is about 5,500 SF. The Ground floor is a parking garage
> of concrete & steel (Type 1a construction) with 4 stories of Residential
> above which constructed of wood (Type 3B Construction). The parking garage
> shall be protected by a Dry Pipe System designed in accordance with NFPA
> 13.
> There is a 2 hour Occupancy Separation between Garage & The Second Floor.
> The Second thru Fifth levels are to be protected by a NFPA 13R Sprinkler
> System. The overall building height measures less than 60' above grade.
>
>
>
> NFPA 13R Scope:  states this standard shall cover ____ "residential
> occupancies up to and including four stories in height in buildings not
> exceeding 60 ft. in height above grade plane."
>
>
>
> Due to the phrase "in Buildings" am I interpreting this correctly?
>
>
>
> Regards,
>
> G. Tim Stone
>
>
>
> G. Tim Stone Consulting, LLC
>
> NICET Level III Engineering Technician
>
> Fire Protection Sprinkler Design
>
> and Consulting Services
>
>
>
>    117 Old Stage Rd. - Essex Jct., VT. 05452
> <https://www.google.com/maps/search/117+Old+Stage+Rd.+-+Essex+Jct.,+VT.+05452?entry=gmail&source=g>
>
> CELL: (802) 373-0638   TEL: (802) 434-2968
>
>               <mailto:[email protected]> [email protected]
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________