Deflector distance isn't a problem, I can either run the branch line up high in 
every pocket/bay or utilize an upright ESFR (Tyco ESFR-17).

I was thinking that the minimum spacing didn't apply when there was an 
obstruction/baffle between the heads (in this case, the legs of the concrete 
tee) and the heads are installed in "every bay channel formed by solid 
structural members". This is specifically allowed in the FM Datasheets, but I 
believe they also have a minimum remote areas size that would require you to 
add sprinklers to the remote area. 

Is the consensus among the group that this building (concrete tees with legs 5 
feet on center) just cannot be protected with ESFR sprinklers per NFPA 13?

And, if that's the case, are we also saying that any time there is a 
beam/obstruction in an ESFR system that the heads on either side of it still 
need to be at least 8 feet apart? You can't have a head 3 feet away on each 
side of the beam (heads 6 feet apart but with a solid obstruction/baffle 
between them)?

-Kyle M

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Mike Hairfield via Sprinklerforum
Sent: Wednesday, December 29, 2021 12:22 PM
To: [email protected]
Cc: Mike Hairfield <[email protected]>
Subject: [EXTERNAL] Re: ESFR - Minimum Remote Area Size

I don’t believe ESFR sprinklers can be installed in a concrete tee building.
Minimum spacing is 8’-0” and what is the deflector distance.
Mike 

Sent from my iPhone

> On Dec 29, 2021, at 2:11 PM, Kyle.Montgomery via Sprinklerforum 
> <[email protected]> wrote:
> 
> I'm dealing with an existing concrete tee building that the owner wants to 
> retrofit with an ESFR system. Heads will be closely spaced due to the 
> obstruction caused by the tees; 5-foot on center. Does NFPA 13 have a minimum 
> remote area size, or is it just 12 heads?
> 
> -Kyle M
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.com/v3/__https://na01.safelinks.protection.outlook.com/?url=http*3A*2F*2Flists.firesprinkler.org*2Flistinfo.cgi*2Fsprinklerforum-firesprinkler.org&amp;data=04*7C01*7C*7C2243e8f422f447e9e98808d9caff0ba5*7C84df9e7fe9f640afb435aaaaaaaaaaaa*7C1*7C0*7C637764019046194532*7CUnknown*7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0*3D*7C3000&amp;sdata=pbf*2BoThaf77nppLZONRpZrs9AwSkwAHo*2FPdId21LXD8*3D&amp;reserved=0__;JSUlJSUlJSUlJSUlJSUlJSUlJQ!!Ba8_KKAT!cFpuCO_w9YY4Ug5JApVoeXhH0dAjA9mRe1AyvYgW_8Szjt_tnI_096ZtrSXQJ6oSgXY$
>  
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!Ba8_KKAT!cFpuCO_w9YY4Ug5JApVoeXhH0dAjA9mRe1AyvYgW_8Szjt_tnI_096ZtrSXQNV76eoU$
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to