I would be addressing this as plastic storage since the liquid is a 
non-flammable/combustible liquid and there is the presence of empty plastic 
containers.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
craig.pr...@jacobs.com | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS



-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Steve Mackinnon via Sprinklerforum
Sent: Wednesday, January 26, 2022 10:03 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Mackinnon <ste...@hartcorn.com>; Scott Futrell <sco...@ffcdi.com>; 
Mike Hairfield <fsl...@msn.com>
Subject: [EXTERNAL] RE: question about Storage height

It's a non flammable, non combustible liquid. Sodium hydroxide 10 N

The storage container and empty vessel are one time use only. There would be no 
cleaning of containers for use again.

Hope this helps.

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Scott Futrell via Sprinklerforum
Sent: Wednesday, January 26, 2022 9:32 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Scott Futrell <sco...@ffcdi.com>; Mike Hairfield <fsl...@msn.com>
Subject: RE: question about Storage height

You didn't mention what the liquid is. If it is a hazardous material as 
recognized by the International Fire Code then the 'empty' container is still 
considered full unless completely cleaned.

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Mike Hairfield via Sprinklerforum
Sent: Wednesday, January 26, 2022 8:08 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Hairfield <fsl...@msn.com>
Subject: Re: question about Storage height

It should be 10 feet even though the other container is empty it's still 
plastic.

Mike
________________________________
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> on behalf 
of Steve Mackinnon via Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Sent: Wednesday, January 26, 2022 9:02 AM
To: sprinklerforum@lists.firesprinkler.org 
<sprinklerforum@lists.firesprinkler.org>
Cc: Steve Mackinnon <ste...@hartcorn.com>; Peter Howard <phow...@hartcorn.com>
Subject: question about Storage height

Good morning all,

We have a storage situation where the liquid commodity is in a 5 foot plastic 
storage cube, with an equally sized empty plastic container below.

The empty container below is only there to act as a spill collection vessel.

The question our office has been banging around, what is the storage height???

Would this be considered 5 feet of storage or 10 feet?

Would you take any exception to the plastic containers (like when we change the 
commodity classification with wood to plastic pallets)?

Thank you in advance
Steven
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__https://na01.safelinks.protection.outlook.com/?url=http*3A*2F*2Flists.firesprinkler.org*2Flistinfo.cgi*2Fsprinklerforum-firesprinkler.org&amp;data=04*7C01*7C*7C0d961840310a423de85308d9e0d49405*7C84df9e7fe9f640afb435aaaaaaaaaaaa*7C1*7C0*7C637788025897874973*7CUnknown*7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0*3D*7C3000&amp;sdata=gZPzEokK*2FC*2FBPf*2FyCzVVjYGR3*2FRAFZEAkLsE2Cn2Qjk*3D&amp;reserved=0__;JSUlJSUlJSUlJSUlJSUlJSUlJSUl!!B5cixuoO7ltTeg!WujZXiMCDFwkNIrrmR8IRgjlaCTGKT7x-mHxMUsZdEIvRqgwJthnftCbEubIYgAaHw$
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WujZXiMCDFwkNIrrmR8IRgjlaCTGKT7x-mHxMUsZdEIvRqgwJthnftCbEuYt1b_c9w$
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WujZXiMCDFwkNIrrmR8IRgjlaCTGKT7x-mHxMUsZdEIvRqgwJthnftCbEuYt1b_c9w$
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WujZXiMCDFwkNIrrmR8IRgjlaCTGKT7x-mHxMUsZdEIvRqgwJthnftCbEuYt1b_c9w$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to