Is the spill container open top? That will be an issue. These sound like
plastic totes. If the liquid is not combustible the empty tote is still a
lot of plastic

Art

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Scott Futrell via Sprinklerforum
Sent: Wednesday, January 26, 2022 9:32 AM
To: [email protected]
Cc: Scott Futrell <[email protected]>; Mike Hairfield <[email protected]>
Subject: RE: question about Storage height

You didn't mention what the liquid is. If it is a hazardous material as
recognized by the International Fire Code then the 'empty' container is
still considered full unless completely cleaned.

Scott
 
Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Mike Hairfield via Sprinklerforum
Sent: Wednesday, January 26, 2022 8:08 AM
To: [email protected]
Cc: Mike Hairfield <[email protected]>
Subject: Re: question about Storage height

It should be 10 feet even though the other container is empty it's still
plastic.

Mike
________________________________
From: Sprinklerforum <[email protected]> on
behalf of Steve Mackinnon via Sprinklerforum
<[email protected]>
Sent: Wednesday, January 26, 2022 9:02 AM
To: [email protected]
<[email protected]>
Cc: Steve Mackinnon <[email protected]>; Peter Howard
<[email protected]>
Subject: question about Storage height

Good morning all,

We have a storage situation where the liquid commodity is in a 5 foot
plastic storage cube, with an equally sized empty plastic container below.

The empty container below is only there to act as a spill collection vessel.

The question our office has been banging around, what is the storage
height???

Would this be considered 5 feet of storage or 10 feet?

Would you take any exception to the plastic containers (like when we change
the commodity classification with wood to plastic pallets)?

Thank you in advance
Steven
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesp
rinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C
01%7C%7C0d961840310a423de85308d9e0d49405%7C84df9e7fe9f640afb435aaaaaaaaaaaa%
7C1%7C0%7C637788025897874973%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJ
QIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=gZPzEokK%2FC%2F
BPf%2FyCzVVjYGR3%2FRAFZEAkLsE2Cn2Qjk%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to